Mains domestic LED lamps on 3-way switch glow faintly in one 'off' arrangement

On my landing are three connected lights. They have 230v LED bulbs. There are three switches - one obviously an intermediate switch. In one of the four 'off' arrangements of the switches, the LEDs glow faintly. Does anyone have a theory on where this current might be leaking to? Thanks.
 
It probably happens only in one of the permutations because of the layout of the common and strapper cores in 3-core & earth cable between the switch points. I.e. If PL and SL are connected to the two adjacent cores lying to one side of the CPC for the whole run, then the capacitive leakage is sufficient to light the lamps. In switch positions that select cores on opposite sides of the CPC, the mutual capacitance is lower and the leakage is too low to have an effect. Remedy as above.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
Nick Willder,
Last reply from
Lucien Nunes,
Replies
2
Views
1,357

Advert

Back
Top