Hi I am working in a hotel and I found that a 3-phase DB was fed by 2 seperate swa cables one containing the 3 phases and the other a seperate neutral and earth I know this is bad practice but can someone tell me why the NIC firm have picked this ad a fault I would not have done this myself it has been installed for over 20 years can any one help thanks
 
Hi I am working in a hotel and I found that a 3-phase DB was fed by 2 seperate swa cables one containing the 3 phases and the other a seperate neutral and earth I know this is bad practice but can someone tell me why the NIC firm have picked this ad a fault I would not have done this myself it has been installed for over 20 years can any one help thanks


What i'm concerned about, is that the OP had no idea about this fundemental rule, and put it down to just bad practice!!!
 
My lad was asked to finish off a PV job, just a few connections mate couple of hours at the most, when he arrived 4 25mm singles all neatly entering a dirty great metal box all neatly installed with stuffing glands the guy that gave him the job wouldn't believe it had been installed incorrectly, and he had been doing it this way for years, makes you wonder doesn't it?
 
My lad was asked to finish off a PV job, just a few connections mate couple of hours at the most, when he arrived 4 25mm singles all neatly entering a dirty great metal box all neatly installed with stuffing glands the guy that gave him the job wouldn't believe it had been installed incorrectly, and he had been doing it this way for years, makes you wonder doesn't it?

It certainly DOES!! ...lol!!
 
Ferro magnetic (steel) enclosures are required to enclose all live conductors including the neutral. Chapter 52 at the beginning somewhere.

Not only the live conductors - but the protective conductor too. Although for SWA that might be the armouring, and the Regulation does oddly allow a separate protective conductor to be run outside the ferromagnetic enclosure in the case of SWA only!
 

Reply to Mains on 3-phase DB in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top