Sorry title was a bit dramatic, but wanted to get as much knowledge as possible.
I was working at a biomass factory today after they had a fire. Extension leads were apparently the cause.
When doing a test at the db I noticed that L1 phase was at 272v to earth. L2 phase was 222v to earth and L3 phase was 240v to earth. Any phase to neutral was 240v. I then carried out a high loop test on all phases and got between 76 and 80 Ohms.(TNC's/PME).
Due to these readings I went to 11kv transformer that is in the building and done the same test a lv side of panel and was still getting same results. I then took a feed out to earth rods/ earth mat of transformer, but was still getting the same figures. I have got past test results that said ze was 0.2 Ohms a couple of weeks ago.
I also noticed when any circuit is turned off you get 30v from earth to neutral and earth to live. Also rcd's are failing to trip on push buttons.
Just wondered if anyone had an explanation for these findings and if so could you please explain in simpletons terms.
Much appreciated in advance
(I'm guessing a problem with neutral at star point of transformer).
 
Ok Thanks. I have tested at every earth point in building and still got same readings. Even at earth mat for transformer.
Another funny thing is that western power said they had an issue with one of their transformers the same time the fire started. However they will not look at this one as it is a private transformer . What the issue was I don't know. He also hasn't got any surge protection on building so wondering if there was a transient voltage or something that has caused some damage!
 
Ok Thanks. I have tested at every earth point in building and still got same readings. Even at earth mat for transformer.
Another funny thing is that western power said they had an issue with one of their transformers the same time the fire started. However they will not look at this one as it is a private transformer . What the issue was I don't know. He also hasn't got any surge protection on building so wondering if there was a transient voltage or something that has caused some damage!

Ask WPD to spill the details of the issue that they had... Also try measuring the voltage between N and true earth ( the brown stuff outside.
 
The guys who installed the transformer are supposed to be coming out tomorrow with a SPECIAL tester , what ever that means. However I wanted to see if you guys knew a possible cause.
 
I have got a trapped nerve in my back at the moment , so having a job to concentrate .
But it sounds to me like a failing neutral on the incomer
 
I will try but my head is just not with it tonight !
If you you have a failing neutral joint on the incomer before the meter , it will give a poor return . On three phase it can find a alternative path through any 3 phase connected equipment . I have seen the variations you have described several times , and each time it was a failing supply neutral .
I have not explained it very well , but I am afraid it is the best you will get out of me tonight
 
Just out of interest could western powers problems have caused this and would it be possible in any way for this to contribute to the fire.
JUST STARTING TO GOOGLE.
 
all kneel before the mighty instr. tech. !

;-)

Finally, some acknowledgement of my mightiness!!!

[ElectriciansForums.net] MAJOR problem with supply...


Instuments, just one of my many skills :)
 

Reply to MAJOR problem with supply... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
714
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
When I was at college doing the 2361 back in the 1980's I still recall to this day the instructor (Mr Wood) saying "Lads I do not want you to...
Replies
10
Views
522
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top