As ever, these days..... RTFM!!
From GS38:
Test equipment
Test probes, clips and leads
9 The test probes, clips and leads used in conjunction with electrical test equipment should be selected to prevent danger. Modern test probes, clips and leads should:
■ conform to the requirements of BS EN 61010-031 or in the case of a 2-pole voltage detector to BS EN 61243-3 (see Further reading);
■ be marked with the rated installation category – CAT II, III, or IV;
■ be marked with the manufacturer’s name or identifying mark; and have the following:
■ probes, and clips, which:
o have finger barriers or are shaped to guard against inadvertent hand contact with the live conductors under test;
o are insulated to leave an exposed metal tip not exceeding 4 mm measured across any surface of the tip. Where practicable it is strongly recommended that this is reduced to 2 mm or less, or that spring- loaded retractable screened probes are used;
o when used with a multimeter, should have suitable high-breaking capacity (hbc), sometimes known as hrc, fuse, or fuses,† with a suitable current rating (usually not exceeding 500 mA), except when used with a loop impedance or RCD tester where a value of 10 A is typically used or a current-limiting resistor and a fuse.**
* BS EN 61010 (see Further reading) defines measurement categories (CAT) as below; these reflect the level of overvoltage that can be expected at the point of measurement:
■ measurement category IV is for measurements performed at the source of the low voltage installation (eg meters, primary overcurrent protection devices etc);
■ measurement category III is for measurements performed in the building installation (eg measurements on distribution boards, socket outlets, permanently connected equipment, etc);
■ measurement category II is for measurements performed on circuits directly connected to the low voltage installation (eg appliances, portable tools, etc).
† Fuses, especially low current (500 mA), can add significant resistance to the test lead (up to 2 ohms). This should be taken into account when using fused leads in conjunction with resistance measuring equipment. When replacing fuses, the correct type and correct current and voltage rating must be used. Glass fuses are not suitable.
** Test equipment which predates the British Standards listed above, or was designed to another standard must be maintained to prevent danger and should comply with the guidance on probes and clips in paragraph 9.