max allowable disconnection times? | on ElectriciansForums
Discuss max allowable disconnection times? in the UK Electrical Forum area at ElectriciansForums.net
R
Ryan Kavanagh
hi guys,
what is the max allowable disconnection time times under fault conditions for kitchen lighting, bedroom socket outlets and also for a shower?
thanks in advnace i appreciate all your help
yes thats what i read but i thought tn systems were most common for domestic uk supply thats were i came to the 0.4sec conclusion.
It very much depends on where you are, in my neck of the woods (Northumberland) I'd say it's about 50/50 TN to TT.
the 5 second rule for TN systems is set at such a level to allow discrimination between protective devices. To have distribution circuits any lower would mean that the tolerances for discrimination would need to be very tight indeed. The earthing on a TN system is said to be reliable and constant, where as a TT system is not. Also prolonged faults in a TT sytem can cause the ground potential to rise, giving a shock risk (the dead horse a few months ago)
Reply to max allowable disconnection times? in the UK Electrical Forum area at ElectriciansForums.net
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
It’s quite common for an electrician to criticise another’s work as you will rarely get everything perfect.