Ryan Kavanagh

hi guys,

what is the max allowable disconnection time times under fault conditions for kitchen lighting, bedroom socket outlets and also for a shower?

thanks in advnace i appreciate all your help
 
I also think (i may be wrong) that this takes into acount that a TT system will only be allowed upto a certain level, and after that then its either a TN sytem supplied, or the customer has HV supplied, and own their own transformer and associated network.
 
the 5 second rule for TN systems is set at such a level to allow discrimination between protective devices. To have distribution circuits any lower would mean that the tolerances for discrimination would need to be very tight indeed. The earthing on a TN system is said to be reliable and constant, where as a TT system is not. Also prolonged faults in a TT sytem can cause the ground potential to rise, giving a shock risk (the dead horse a few months ago)

so why do the tolerances in TT discrimination not differ? from TN and surely the tolerances would need to be greater if the time was shorter
 
Hi John

thing is RCD only disconnects L-E faults not L-N the CB does that so why is the disconection different when the same CB are used
so why do TT not have same disconnection time as TN
must be a logical reason , one reason could be the unstable parameteres as you mentioned.......
 
It does have a lot to do with the unstable parameters mentioned, such as poor earthing, lack of bonding etc.

Essentially the shock voltage difference between an TN & a TT system is roughly double, i.e a TN system with a good, reliable, low impedance fault path, with both line & CPC of the same CSA (disregard T+E here), would have a shock voltage of roughly 115V

TT would be almost as makes no difference be 230V which would travel through the installation & via the high impedance earth electrode, which is why we must reduce the disconnection time for clearance of an L-E fault.

I believe the 5s rule for TN systems was to allow the continued use of a 3036 re-weireable type fuse. It's reduced to 1s for TT to allow for discrimination to be achieved.
 

Reply to max allowable disconnection times? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
693
  • Question
It’s quite common for an electrician to criticise another’s work as you will rarely get everything perfect.
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top