hi guys,

what is the max allowable disconnection time times under fault conditions for kitchen lighting, bedroom socket outlets and also for a shower?

thanks in advnace i appreciate all your help
 
I also think (i may be wrong) that this takes into acount that a TT system will only be allowed upto a certain level, and after that then its either a TN sytem supplied, or the customer has HV supplied, and own their own transformer and associated network.
 
the 5 second rule for TN systems is set at such a level to allow discrimination between protective devices. To have distribution circuits any lower would mean that the tolerances for discrimination would need to be very tight indeed. The earthing on a TN system is said to be reliable and constant, where as a TT system is not. Also prolonged faults in a TT sytem can cause the ground potential to rise, giving a shock risk (the dead horse a few months ago)

so why do the tolerances in TT discrimination not differ? from TN and surely the tolerances would need to be greater if the time was shorter
 
Hi John

thing is RCD only disconnects L-E faults not L-N the CB does that so why is the disconection different when the same CB are used
so why do TT not have same disconnection time as TN
must be a logical reason , one reason could be the unstable parameteres as you mentioned.......
 
It does have a lot to do with the unstable parameters mentioned, such as poor earthing, lack of bonding etc.

Essentially the shock voltage difference between an TN & a TT system is roughly double, i.e a TN system with a good, reliable, low impedance fault path, with both line & CPC of the same CSA (disregard T+E here), would have a shock voltage of roughly 115V

TT would be almost as makes no difference be 230V which would travel through the installation & via the high impedance earth electrode, which is why we must reduce the disconnection time for clearance of an L-E fault.

I believe the 5s rule for TN systems was to allow the continued use of a 3036 re-weireable type fuse. It's reduced to 1s for TT to allow for discrimination to be achieved.
 

Reply to the thread, titled "max allowable disconnection times?" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top