Just double checking calcs if anyone bored!

So for a block of 3 flats with no gas services- all flats same. +communal stairs over 2 floors (LED light few small panel heaters)

Flat:
Kitchen Ring (32a) (32)
Ring (32a) (12.8)
Oven (20a) (13)
Hob (32a) (16.6)
Immersion (16a) (16)
Lights1 (6a) (3.9)
Lights2 (6a) (3.9)
Heating1 (20a) (2x Dimplex Monterey Panel Heater - 2000w) (15)
(Heating2 (20a)(2x Dimplex Monterey Panel Heater - 2000w) (15)
(heating3 (20a) ((2x Dimplex Monterey Panel Heater/towel rail - 1000w) (15)

Do I stick with 32+32+20+32+16+6+6+20+20+20 x0.4= 81.6amps

Advise a TPN 100a supply is needed- and stick a 4way Ryefield in with 3x 100a fuses (flats)+ 1x 60a (L/L)

OR
32+12.8+13+16.6+16+3.9+3.9+13.7+13.7+13.7=139.3!!!!!

my heads telling x 0.4 would be fine- but I know thats just the quick/lazy method
appreciate any advise
 
Doesn't seem right
No, and it probably is not. It is just calculating for a theoretical load supposing a person in the flat had hypothermia tendencies and kept tropical things like snakes, and likes to eat 14 times a day (including the boa, fatted calf!) with a full roast in the oven and on top who also has a morbid fear of the dark and hates anything but incandescent filament lamps so has all the lights on and who is constantly filthy so has to keep loads of hot water to keep cleaning them and their clothes, and loves hot towels, never mind about their partner.
 
m
No, and it probably is not. It is just calculating for a theoretical load supposing a person in the flat had hypothermia tendencies and kept tropical things like snakes, and likes to eat 14 times a day (including the boa, fatted calf!) with a full roast in the oven and on top who also has a morbid fear of the dark and hates anything but incandescent filament lamps so has all the lights on and who is constantly filthy so has to keep loads of hot water to keep cleaning them and their clothes, and loves hot towels, never mind about their partner.
my ears are burning
 
No, and it probably is not. It is just calculating for a theoretical load supposing a person in the flat had hypothermia tendencies and kept tropical things like snakes, and likes to eat 14 times a day (including the boa, fatted calf!) with a full roast in the oven and on top who also has a morbid fear of the dark and hates anything but incandescent filament lamps so has all the lights on and who is constantly filthy so has to keep loads of hot water to keep cleaning them and their clothes, and loves hot towels, never mind about their partner.
Perhaps PhotonicInduction wrote that part of the OSG ?
 

Reply to max demand for flats in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
197
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
248
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
346

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top