Max length of meter tails | on ElectriciansForums
Discuss Max length of meter tails in the UK Electrical Forum area at ElectriciansForums.net
Bradwell, Derbyshire
Ive been asked to look at the electrical installation at a large 5 bed property with an attached annexe that the owners are converting into a 2 bed holiday let.
There's one supply cable that comes into the annexe for the entire property .
This is currently routed via a single meter to a CU .
2 sub boards are run from this , 1 for the annexe and 1 for the main house.
Trouble is , the house CU (20mtrs away) has been run using 10mm cable which is obviously insufficient. I would want to run this using 25mm CSA meter tails instead (after doing cable calcs) , via a separate meter , directly to the house's CU .
Is this allowed , can't find the regs covering max length of meter tails .
I've loads of other questions but will see what replies I get as they may answer some of these questions .
A big thank you if you've read this far !
i think that there's no reg. to cover that, but DNOs usually request/demand that tails over 3m in length are protected by a switch/fuse with the fuse being of a lower rating than their supply fuse.
This is covered by the regs. This is a circuit like any other and should have adequate overcurrent and fault protection. The DNO usually allow use of their fuse up to 3m. See 433.3.1 (iii)
The 3m rule has basis in the regs also as the maximum length for a cable with the device for protection of overload not at origin of the circuit. 433.2.2 (ii)
Reply to Max length of meter tails in the UK Electrical Forum area at ElectriciansForums.net
You would treat it as a TT installation.
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...