can some one remind me how do i work out the max power i can put on to a distribution board in a house and also in a factory
is it add all the RCD and divived it by 100ma on the house Thanks :eek:
 
Last edited by a moderator:
Re: Max on a CB

Ok, diversity is as follows:

Lighting - 66% of total current demand for each circuit
Power - 100% of the first ring circuit + 40% of all other circuits
Cooker - 10A + 30% of remaing rated current + 5% if the CCU has a socket outlet
Shower - No diversity allowable
Instantaneous water heater - 100% of largest heater + 100% of second largest + 25% of of any others
Thermostatically controlled water heater - No diversity allowable
Underfloor heating - No diversity allowable


As a rule of thumb if you total all the circuit breakers (not RCD's) in the consumer unit and multiply by 0.4 you will come up with an rough total of max load.
 
Last edited by a moderator:
Re: Max on a CB

Ok, diversity is as follows:

As a rule of thumb if you total all the circuit breakers (not RCD's) in the consumer unit and multiply by 0.4 you will come up with an rough total of max load.

I've just worked out the Max CB (sic) :cool: on my own personal blackpool illuminations ( I have teenagers) & need 111Amps!:eek: ; No wonder I get letters of thanks from the chairman of E-on. lol
 
daver in a house the smoke alarms are possibly of a lighting circuit or if they are wired alone the load is very small just checked my alarms 0.03a 30ma as its that low i wouldnt even factor it into the diversity calculation unless i had a huge amount 20+ sort of region.

As for the emergency lights I=p/v so 16 /230 =0.06 amps depends how many you have wwhether you calculate it in again either linked of lighting or seperate circuit.
 

Reply to Max on a DB in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
693
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
785

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top