One little word of warning, if you are measuring your Zs very close to a transformer, you may find you get false (high) readings due to the impedance of the transformer windings. I have done a little spreadsheet that will calc the Zs at the incoming terminals of a switchboard fed by a transformer. Let me know if you would like this.
Hi Andy if you could pass this on would be great
Reply to Max Zs for Bs88-2 630amp fuse in the Talk Electrician area at ElectriciansForums.net
    • Friendly
This is one of my bug bears as it's very easily overlooked with temporary installations unless they are properly inspected and tested under...