Max Zs for TT. | Page 2 | on ElectriciansForums

Discuss Max Zs for TT. in the UK Electrical Forum area at ElectriciansForums.net

dlt27

-
Joined
Jul 4, 2011
Messages
196
Reaction score
30
Don't know if I'm being a proverbial div, but could someone tell me the max Zs for 80A 1361( distribution cct )on a TT system with disconnection time of 1.0 sec. Thanks.
 
Don't know if I'm being a proverbial div, but could someone tell me the max Zs for 80A 1361( distribution cct )on a TT system with disconnection time of 1.0 sec. Thanks.

0.40 Ohms
So wouldn't be achievable on a TT system, meaning disconnection times would need the use of an RCD so!!
Looking at 1 second disconnection times for distribution circuits, and 0.2 seconds for all others.
With a 100ma Rcd employed a max value of 500 ohms.
All that said, stability issues are considered relevant with anything over 200 ohms by BS 7671
Or as the NICEIC would advise (They make there own rules up) 100 ohms.
Final circuits are often quoted 1667 ohms when disconnection times are afforded by a 30ma rcd but thats generic and I personally prefer the tabulated values.
That's my take, hope it helps. :icon12:
 
Last edited by a moderator:
0.40 Ohms
So wouldn't be achievable on a TT system
, meaning disconnection times would need the use of an RCD so!!
Looking at 1 second disconnection times for distribution circuits, and 0.2 seconds for all others.
With a 100ma Rcd employed a max value of 500 ohms.
All that said, stability issues are considered relevant with anything over 200 ohms by BS 7671
Or as the NICEIC would advise (They make there own rules up) 100 ohms.
Final circuits are often quoted 1667 ohms when disconnection times are afforded by a 30ma rcd but thats generic and I personally prefer the tabulated values.
That's my take, hope it helps. :icon12:

It would at Trev's home! ;)
 
If you have a stable sub 1 ohm TT system, i wouldn't be still using the 1 sec and 0.2 sec values, i'd be quite happy to use TN disconnecting times.... And getting a TT system below 1 ohm is achievable if you go about things in the right way. The last time i checked my own houses TT system in Cyprus last year, was 0.88 and has been consistently dropping for the last few years. I wouldn't call the ground type particularly good either....
 
Last edited by a moderator:

Reply to Max Zs for TT. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
705
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top