Don't know if I'm being a proverbial div, but could someone tell me the max Zs for 80A 1361( distribution cct )on a TT system with disconnection time of 1.0 sec. Thanks.
0.40 Ohms
So wouldn't be achievable on a TT system, meaning disconnection times would need the use of an RCD so!!
Looking at 1 second disconnection times for distribution circuits, and 0.2 seconds for all others.
With a 100ma Rcd employed a max value of 500 ohms.
All that said, stability issues are considered relevant with anything over 200 ohms by BS 7671
Or as the NICEIC would advise (They make there own rules up) 100 ohms.
Final circuits are often quoted 1667 ohms when disconnection times are afforded by a 30ma rcd but thats generic and I personally prefer the tabulated values.
That's my take, hope it helps. :icon12:
I ain't buying it until I need to mate. The current one is chock a bloc full of errors. No thanks IET, I'll wait until they're corrected and then I'll invest.
If you have a stable sub 1 ohm TT system, i wouldn't be still using the 1 ohm and 0.2 ohm values,