Hello all, i'm currently doing level 3 2330 and am getting a little confused with the different max Zs values in the OSG and the Regs. I'd appreciate any advice .
Would i be right here
I use the max Zs values in the OSG for installation design as these are lower to account for the reduced resistance of cold conductors, as opposed to the operating temperature max Zs values in the regs.
ie. Zs = Ze+[(R1+R2) x multiplier x length
1000
Does this mean that when subsequently doing a live Zs test, I would check the results against those in the regs instead of the OSG. Or am i wrong to think that an energised installation means that the conductors are at operating temperature? Should i stick to the OSG when testing too?
Would i be right here
I use the max Zs values in the OSG for installation design as these are lower to account for the reduced resistance of cold conductors, as opposed to the operating temperature max Zs values in the regs.
ie. Zs = Ze+[(R1+R2) x multiplier x length
1000
Does this mean that when subsequently doing a live Zs test, I would check the results against those in the regs instead of the OSG. Or am i wrong to think that an energised installation means that the conductors are at operating temperature? Should i stick to the OSG when testing too?