Hi might be a stupid question but somone might have the answers.
TNS systems and TT where the Ze of the installation is a lot higher than a Ze <0.35 of a TNCS system, how do you comply max Zs of a MCCB in a panel board disconnection time of 5s? Most data manufacturers instruction give really low max Zs values which are not achievable?
Is the only way round this to have combined MCCBS with earth leakage or earth leakage relays /shunt trips .
I also read something in the regs book about omission of RCDS for fault protection, use of supplementary bonding. Calculation required and something to do with touch voltage ?
So many EICRS in the past the disconnection time has not been met if manufacturers data found , otherwise I have LIM it if not data.