Ive asked this before but never really got any replies, but now i need a definte answer.

ive been told by a good source that if the zs reading taken at a socket for eample is over the max allowed in table 41 b in the regs, as long as its on an rcbo its still safe and complies with regulations.

can anyone on here confirm this please and give reasons why.

i have a number of ringmains on type c rcbo which are over max zs values but i can not get type b rcbo for weeks, this is a big issue for me atm.

help please, i have the client giving me major hassle.

thanks.
 
Have you looked in the OSG and the regs to see what they require?

What Ze did you get?

This may play a large part in why your Zs readings are out.

I would say yes its fine, however, i dont have the regs with me to double check at the mo.
 
The guy from the NIC pulled me on this last year and told me that the table on page 50 covers all 61008 and 61009 RCDs not only in TT systems. That being the reason why if you come across a circuit that you can't meet the maximum Zs you should install an RCD so that you can meet the disconnection time.
 
The guy from the NIC pulled me on this last year and told me that the table on page 50 covers all 61008 and 61009 RCDs not only in TT systems. That being the reason why if you come across a circuit that you can't meet the maximum Zs you should install an RCD so that you can meet the disconnection time.


I thought the use of an RCD was allowed, but only in certain circumstances (high efli) but it should ideally be sorted if the readings were high?

Does it state that on P50?

I thought (havent got my book handy) that there were values for TN systems and and value for TT systems.

Sounds to me like the NIC are quoting their own regs again:D:D
 
Hey.

I was always taught/told that you meet your Zs values come hell or high water by college lecturers, colleagues and the NIC alike if the system of earthing is provided by the DNO i.e TN-S, TN-C-S.

If you cant then we either change the breaker or cableing to suit.

In an industrial application RCD's are not always a feasible remedy.

Another point to to consider is that these requirements should have been assured at the design stage.

With TT I absolutely agree as there is no way the values can be met.

IMO unless the circuit needs to be RCD protected fitting one because your Zs values are out and not on a TT system is the incorrect way round it and either more consideration should have been given at design stage or there may be an underlying problem which needs addressing.


I have my tin hat on and am running for cover as you read.:D
 
I totally agree lenytheloon but i am just telling you what Mr NIC told me on my last visit. He initially pulled me on my paper work for putting the "incorrect values" in the maximum Zs box when the circuit(s) are RCD protected then started to preach the formula on page 50 of the 17th edition.
He even went on to ask the maximum Zs question on one of the site visits when testing just to make sure i was listening and had understood him.
 

Reply to Max zs on rcbo in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
223
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
683
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
632

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
234
  • Question
UPDATE, after contacting Paypal, uploading all the emails and evidence the sending the transformer back I have now received a full refund...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top