Hi just wondering what people are noting as there max permitted zs reading on test results sheet for TT systems? 200ohms or 1667ohms?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Max zs readings for TT in the UK Electrical Forum area at ElectriciansForums.net
I go by what the dno insist on and the only figure that is realistically acceptable <200
Which DNO insists on less than 200?
I've never heard of this before and considering the DNO have nothing to do with a consumers own earth electrode I don't see how it's any of their business getting involved?
If you enquire a DNO will give you a figure of 21ohms max for their side of things.
Really and no 1667?If it helps the NICEIC online certification gives you 200 as the autofill value to select on their forms
Yes pretty sure, got one in progress I'll take a picture of it laterReally and no 1667?
Me too sorry Ruairi I was thinking of Ze as wellJust realised that this thread was about Zs not Ze or Ra..
My comment about the DNO figure of <200 was Ze..
There is no requirement for Zs to be of a value to operate the OCPD within the required time in the event of a fault to earth. The preferred means of earth fault protection on a TT is an RCD (411.5.2) and the maximum Zs value will be in accordance with table 41.5. (411.5.3).
The maximum value whether you like it or not is 1667 ohms for a 30ma RCD and that is the value to be recorded on a cert for a 30ma RCD.
No you didn't.
By the way, have you found that reg number for the other thread yet?
An RCD isn't an overcurrent protective device.In this insta
No I haven't.
In a TT an RCD would be used for fault protection so would therefor be the OCPD. As such the maximum Zs for the rated RCD would come into effect.
As I said - this is what I said.....
An RCD isn't an overcurrent protective device.
It is when it is a BS 61009.
Of course, but that's not the RCD element. (And BS EN 61009 to be pernickety.)It is when it is a BS 61009.
Of course, but that's not the RCD element. (And BS EN 61009 to be pernickety.)
You would also need to use a different number then as 61009 is still the harmonised Standard. And I voted to leave the EU in the referendum too.I just voted for the Brexit Party so removed the EN.
In Malta we have an upper limit of 50Ω (RA). TT is by and large the most commonly found earthing system here. It is that low because there is a high probability of it increasing as most of the ground is some form of limestone.Hi just wondering what people are noting as there max permitted zs reading on test results sheet for TT systems? 200ohms or 1667ohms?