Hi just wondering what people are noting as there max permitted zs reading on test results sheet for TT systems? 200ohms or 1667ohms?
 
I go by what the dno insist on and the only figure that is realistically acceptable <200

Which DNO insists on less than 200?
I've never heard of this before and considering the DNO have nothing to do with a consumers own earth electrode I don't see how it's any of their business getting involved?

If you enquire a DNO will give you a figure of 21ohms max for their side of things.
 
Which DNO insists on less than 200?
I've never heard of this before and considering the DNO have nothing to do with a consumers own earth electrode I don't see how it's any of their business getting involved?

If you enquire a DNO will give you a figure of 21ohms max for their side of things.

The Manx dno
 
Like Dave said it’s not their earthing connection, it’s upto the installer and the installer alone to determine the suitability of the electrode they install
 
There is no requirement for Zs to be of a value to operate the OCPD within the required time in the event of a fault to earth. The preferred means of earth fault protection on a TT is an RCD (411.5.2) and the maximum Zs value will be in accordance with table 41.5. (411.5.3).
The maximum value whether you like it or not is 1667 ohms for a 30ma RCD and that is the value to be recorded on a cert for a 30ma RCD.

In this insta
No you didn't.
By the way, have you found that reg number for the other thread yet?

No I haven't.

In a TT an RCD would be used for fault protection so would therefor be the OCPD. As such the maximum Zs for the rated RCD would come into effect.

As I said - this is what I said.....
 
In this insta


No I haven't.

In a TT an RCD would be used for fault protection so would therefor be the OCPD. As such the maximum Zs for the rated RCD would come into effect.

As I said - this is what I said.....
An RCD isn't an overcurrent protective device.
 
Hi just wondering what people are noting as there max permitted zs reading on test results sheet for TT systems? 200ohms or 1667ohms?
In Malta we have an upper limit of 50Ω (RA). TT is by and large the most commonly found earthing system here. It is that low because there is a high probability of it increasing as most of the ground is some form of limestone.
 

Reply to Max zs readings for TT in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
929
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
705

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top