Discuss Max Zs readings where circuits are protected by 30ma RCD's in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
i will contine to enter the BS7671 values until someone higher up the food chain tells me i'm wrong.
as a little aside to the rights and wrongs of what to enter
RCDs and Indirect Contact Shock Protection
Indirect contact protection by fuses or circuit-breakers is dependent on the earth loop
impedance being within the parameters laid down by BS 7671. Where this cannot be
achieved or where there is some doubt about the consistency, then an alternative method
is required. It is in this situation that the residual current device can offer distinct
advantages over conventional overcurrent protection for indirect contact shock
protection.
The basis of RCD protection in this situation is to ensure that any voltage, due to earth
fault currents, that exceeds 50V is immediately disconnected. This is achieved by choosing
an appropriate residual current rating and calculating the maximum earth loop impedance
that would allow a fault voltage of 50V. This is calculated by using a simple formula given in
BS 7671 Regulation 413-02-16.
Zs x IΔn ≤ 50
Where Zs is the earth fault loop impedance (ohms)
IΔn is the rated residual operating current of the RCD (amps)
therefore a simple calc to arrive at the max zs is
zs = 50 (volts) / rated residual of rcd say for this example 30 ma
therefore max zs for a 30ma rcd (not time delayed) is max zs = 50 / 0.030 = 1666.67 ohms
although as some have said I would not be walking away if the zs reading was anywhere near that, nobody should
Agree to what you have written but not sure why you are giving the 16th edition reference?? when it should be
i will contine to enter the BS7671 values until someone higher up the food chain tells me i'm wrong.
And that's an informed common sense approach that I will also continue to adopt.
This 1667 as a maximum permissable Ze is IMO a very dangerous approach. Sure the calculations stack up in theory, but in adopting these figures you are going down the slippery road of becoming totally reliant on the reliability of the RCD.
A possible way around could be to put more emphasis on the importance of the R1 + R2 readings rather than max Ze.
But when you have maximum Ze's permissable as 1667 in black and white, there really is nothing to stop the less informed from pointing a finger at that statement and saying , sorry but its within the value stated. End of.
Someone is going to die as a result of a failed RCD one day, and suddenly you will see 1667 disappear and the whole situation/regulations re-written as a result.
I have noticed, a lot of max Zs readings on test certs (Where RCD's are applicable) are being blanket recorded at 1667 ohms.
On a personnel note I consider this to be poor practice, and prefer to see max Z's taken from tables 41.2 41.3 and 41.4 of chapter 41 of the good old guide.
My reasons are that 1667 is an unrealistic figure in most cases. and doesn't promote a true solid reliable earth fault return path (Like in the good old days before RCD reliance)
We all know that RCD's offer suplementary shock protection, and thats fair enough but chucking 1667 around like conffetti detracts from what a proper earth fault path is really all about.
Maybe I'm getting padantic in my old age, but its one of those things that bug me.
And if an RCD fails its nice to know the earth fault path will be low enough to take out the overcurrent device before touch voltages rise to a point that Zap's people.
RCD or no RCD. (TT aside that is)
(Rant over)
The only important figure is the measured Zs of the circuit, wirepuller is absolutely correct in what he posted.
If I see a PIR with say a lighting circuit protected by a BS60898 B 6 with a measured Zs of 6 Ohms, immediately alarm bells are ringing and I just know something isn't right, even though the max Zs for the device is over 6 Ohms!
This is competency and conversely, when I see a circuit protected by say a BS61009 C 32 and the max Zs has been entered as 0.71 Ohms then I immediately become a little less confident in the quality of the PIR because that is NOT the maximum Zs for that device.