Luke1989

Hi

Would anyone be able to help me,
Max zs value for type c 32amp RCBO on PME system- 0.72/0.58 or 1776 ohms?

Any help would be appreciated
 
The RCD is additional protection only. What would happen if the RCD failed? Whilst they are great as additional protection, they should not be relied upon as the sole means of protection, as you effectively would be doing if you went with such a high Zs figure! The MCB would become basically just a switch!
 
you need to design the circuit so that the max. Zs is as specified for the OCPD, but there's nothing to say you can't enter 1667 in your SOTR.
 
This i suppose very much depends on whether this is a ''New Circuit'', or an existing circuit that's been altered etc. It seems if existing it's OK to rely on the 1667 ohms of an RCD!! Not my way of doing things, i might add, i would always find the reason for exceeding Max Zs and rectify as needed/required. But if this is for say, a periodic test report purpose, going by BS7671 the circuit conforms as such!!!!! lol!!
 
Agree with previous post. The RCD is there for additional protection, correct installation methods being meet would mean correct/complying Zs values. Don't use RCD's as a cheat to justify high Zs readings, Investigate as there could be loose connection etc......
 
This i suppose very much depends on whether this is a ''New Circuit'', or an existing circuit that's been altered etc. It seems if existing it's OK to rely on the 1667 ohms of an RCD!! Not my way of doing things, i might add, i would always find the reason for exceeding Max Zs and rectify as needed/required. But if this is for say, a periodic test report purpose, going by BS7671 the circuit conforms as such!!!!! lol!!
not in my world it dont...

i would certainly be noting it...
 
There's right, there's wrong and then there's the grey area. As has been said before I'm sure it's used to comply for tt installs!! But I ask this, if the Zs is too high then why? R1&R2? So what about short circuit impedance? If single phase and all the same conductor size and you can't meet Zs then you ain't gonna meet SC.
 
There's right, there's wrong and then there's the grey area. As has been said before I'm sure it's used to comply for tt installs!! But I ask this, if the Zs is too high then why? R1&R2? So what about short circuit impedance? If single phase and all the same conductor size and you can't meet Zs then you ain't gonna meet SC.
no...

whats Zs got to do with Zpn/Zpp?
 
His Reply "Your comment is noted but look at 411.4.9 which refers to 411.3.2.2 which obviously enable use of table 41.5, regarding MCB part of the RCBO this will only used for against overload currents and fault currents in accordance with chapter 43. Which means RCBO is not just a switch. Which is all subject to RCBO tripping times in accordance with reg's" Thoughts?
 

Reply to Max Zs value in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
920
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
260
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
705

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top