yeah both aren't really needed if you just do the simple equation.I use the big blue book for max zs not the OSG.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Max zs values in the Electrical Engineering Chat area at ElectriciansForums.net
yeah both aren't really needed if you just do the simple equation.I use the big blue book for max zs not the OSG.
Those are your cases for a 5s disconnect time, subject to thermal limits on the cable (e.g. adiabatic check).Yep but what 5 second requirement I can't see one except 5 sec is for distribution circuits of & above 32amp ?
Except when the simple equations is very wrong. Yes, if you know it is a B-curve MCB, but in other cases you can get it wrong by a factor of 2 or so.yeah both aren't really needed if you just do the simple equation.
yeah looking at the book is much quicker then pulling a calu out .yeah both aren't really needed if you just do the simple equation
The OSG book in Appendix B has tables that include the typical adiabatic limit for the common CPC sizes so it is your easiest option for selecting an OCPD when desiging something like a garage CU feed, or verifying an existing OCPD and measured Zs is reasonable.Those are your cases for a 5s disconnect time, subject to thermal limits on the cable (e.g. adiabatic check).