What would be the maximum amount of Branches from a Socket on a Radial that you would find acceptable?

I've seen 4

I'm not talking about Design or being Tidy or keeping it nice for testing but how many would you say No that's just too many?
 
Last edited:
Are you referring to sockets on a spur off a ring final circuit

As far as i understand it, if it is an unfused spur then only 1 double gang socket is permitted

If using a F.C.U then I think you can have as many as you like as the cable is over load protected by the fuse in the F.C.U.

If more sockets are added to an unfused spur there is no overload protection for the cable, and it can be easily overloaded and is therefore a fire risk
 
If it is a radial circuit, then the practical limit will be the maximum conductors that can be terminated in a socket's terminals. Other limits are the total load on the added branches, given the maximum current set by the Circuit Protection Device.
 
Agreed. It doesn’t matter as long as the cable and OCPD are correct.
One in, one out is best practice.

a lighting circuit is a radial. Looping in at switch or ceiling rose is designed as one in, one out.... but the old JB could have any number of switches being fed from one live cable
 
Personally 1 or 2. This is very common in French wiring systems and presents a cauchemare as the French say in terms of testing, so the less the better I would say. I am not aware of any limit in BS7671 to branches in radial circuits. If you are discussing Ring Final Circuits there is a nice diagram showing how many spurs one can add to such a circuit which is finite.
 
Personally 1 or 2. This is very common in French wiring systems and presents a cauchemare as the French say in terms of testing, so the less the better I would say. I am not aware of any limit in BS7671 to branches in radial circuits. If you are discussing Ring Final Circuits there is a nice diagram showing how many spurs one can add to such a circuit which is finite.
There is a limit isn't there in France? or other European Country's?
 

Reply to Maximum Branches from Socket on Radial that's acceptable. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Luckily when I rejigged the socket to fit the fcu next to it, it meant the original ring wiring reached, i put the socket on the ring and took a...
    • Like
Replies
8
Views
1K
  • Question
Good point, they do look a bit 6mm-ish when you mention it, and that is not going to last long enough for a D63 to trip! It might, on a good day...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top