can someone please help me with this question

There is a 40A BS88 fuse, protecting a 10mm cable with a 4mm Earth, it is wired to Reference method C, supply is TNS and it is protected by a 30mA RCD. What is the maximum length the cable can be?

(thats all the info i have! I haven't been to collage for couple of years now and cant remember how to do it )
 
VOLTAGE DROP

The maximum permitted volt drop measured from the incoming supply is 3% for lighting circuits and 5% for all other circuits. p358

230v x 3% = 6.9v

230v x 5% = 11.5v
 
Thought I was going mad for a minute and somebody had removed my post.

This question was also posted HERE which is where I replied to it.

Ring circuit

4 x (Max Zs - Ze) Ă· ((R"1 + R"2) x Cr)


Radial

(Max Zs - Ze) Ă· ((R"1 + R"2) x Cr)


R"1 + R"2 = Resistance per meter of Line & Cpc conductors
Cr = Correction factor for conductor operating temp of 70°C

So lets assume your Ze is 0.8 (max for TN-S). The max Zs for a 40A BS88 fuse is 1.35Ω and the R"1 + R"2 of 10/4.0mm² cable is 6.44mΩ per meter.

The calculation would be:

(1.35 - 0.8) Ă· ((6.44/1000) * 1.2) = 71m

However most maximum circuit lengths are limited by Voltage Drop and the voltage drop of 71m of 10mm² cable carrying 40A is 12.5V which exceeds the 11.5V (5%) maximum VD for a power circuit.

VD = mV/A/m x Length x Current
VD = (4.4/1000) x 71 x 40 = 12.5V


So you would need to work out the max length for Voltage Drop

Ring

4 x (Max VD x 1000) Ă· (mV/A/m x Current)


Radial

(Max VD x 1000) Ă· (mV/A/m x Current)


So for your circuit the calculation for VD would be

(11.5 x 1000) Ă· (4.4 x 40) = 65m
 
Last edited by a moderator:

Reply to Maximum Cable Length?? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
155
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
969
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
632
  • Question
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...
Replies
2
Views
267

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top