Maximum demand | on ElectriciansForums
Discuss Maximum demand in the Australia area at ElectriciansForums.net
B
blenki
Hi , when filling in the Maximum demand on the EIC do you guys work out everything based on diversity or do you add up all the MCB's then multiply by 0.66. I keep hearing different versions ,some people just put down the cut out fuse value
The maximum demand will usually only be the fuse value as it cat pull anymore than that!
To be honest, i dont think there is a strict requirement to be spot on.
I know some sparks put down the biggest MCB size.
Hi Blenki
What i do is turn everything off in the house and use a clamp meter on meter-cu line and turn everything on in the kitchen (cooker/hob/toaster/mike/lights/all sockets plug in something and switch on ) this should give you the total load of the property.
Regards
Kung.
norm find its about 54amps for a 3 bed house.
Thanks lads , ive got part p assessment coming up and i want to make sure i can answer him if he asks , il probably work out all the diversitys of each circuit then add them up. just wondered if you lads who have been in the trade a while have a quicker way of doing it
problem i got is with 2x32a ring circuits (100% of first ring then 40% of second)
1x32a boiler circuit (assuming 100% diversity)
1x32a cooker circuit (cooker rated at 30a before diversity)
2x6a light circuits (around 8x 100w lamps on each circuit)
I GET JUST OVER 100A IF IM DOING IT RIGHT
If the boiler circuit is only doing a boiler,pump,controls could that be reduced to 16a or less.
I was under the impression that you should take account of diversity when working out maximum demand.(tin hat on). If you apply diversity to the cooker and 2nd ring your total is still less than 80A even if there is a socket on the cooker point.
Hi Blenki
cooker is first 10A then 30% of the rest of it (plus 5A if there is a socket outlet on the cookerpoint). Lighting is 66% of max. Ring is 100% of first one and 40% of second.
you said cooker was 30A so that is 10A plus 30% of 20 = 16A ( or 21A if there is a socket outlet)
first ring 100% = 32A
2nd ring is 40% of 32A = 12.8A
Lighting 800w/230V=3.5A x2=7A X 0.66% = 5A
total demand = 66A ( or 71A if there is a socket outlet on cooker)
(rounded figures up)
hi pushrod thats the way i worked it out , but you have missed out the boiler circuit (i allowed for 32a worst case scenario ) as i dont know what the boiler is taking. i cant see it taking 32a so it should be under 100a max demand. Thanks for the reply
Reply to Maximum demand in the Australia area at ElectriciansForums.net
Jumping on and off jobs can be tough going when you're less than confident as every time you go back it's like a new job. that you know little...
nicebutdim
N
Tile adhesive just not setting Hi all, New to this forum and an amateur DIY'r. Got a problem I'm hoping that someone can help me with as I'm...
superfuel