Hello,
I am assisting my supervisor and getting some first hand experience of completing certification by filling in an electronic copy of an EIC, working from a handwritten circuit schedule with test results and my memories of the installation work.
I am at home so cannot ask him for advice at this moment.
This question also satisfies my broader desire to develop a thorough understanding of the correct requirements according to BS 7671.
So - I am filling in an EIC for an installation with a TT earthing system and
I am not sure what to record as the maximum permitted Zs value for each circuit.
The circuits are supplied from a consumer unit with dual 30 mA RCDs (BS EN 61008-1) and a selection of BS EN 60898 type B MCBs.
Where a TN earthing system is used, this is of course easy to do, by referring to the values in BS 7671 table 41.3.
I am struggling to understand what I should be entering as the maximum permitted values for a TT installation.
I note the following:
- The reason for calculating, measuring and checking Zs values is to ensure the correct operation of ADS.
- The maximum disconnection time for final circuits 32 A or below is 0.2 s (TT) instead of 0.4 s (TN installations).
- An RCD can be used for fault protection on a TT installation. The maximum earth fault loop impedance for an RCD being calculated from the residual current rating and a touch voltage of 50 V.
I will be honest, I find the BYB difficult to use at times when trying to determine an answer for myself.
With this matter for example, I have been reading through Chapter 41 and it's sending me in circles, with one regulation referring to another and not really arriving at a clear answer.
Any input would be much appreciated.
Thanks.
I am assisting my supervisor and getting some first hand experience of completing certification by filling in an electronic copy of an EIC, working from a handwritten circuit schedule with test results and my memories of the installation work.
I am at home so cannot ask him for advice at this moment.
This question also satisfies my broader desire to develop a thorough understanding of the correct requirements according to BS 7671.
So - I am filling in an EIC for an installation with a TT earthing system and
I am not sure what to record as the maximum permitted Zs value for each circuit.
The circuits are supplied from a consumer unit with dual 30 mA RCDs (BS EN 61008-1) and a selection of BS EN 60898 type B MCBs.
Where a TN earthing system is used, this is of course easy to do, by referring to the values in BS 7671 table 41.3.
I am struggling to understand what I should be entering as the maximum permitted values for a TT installation.
I note the following:
- The reason for calculating, measuring and checking Zs values is to ensure the correct operation of ADS.
- The maximum disconnection time for final circuits 32 A or below is 0.2 s (TT) instead of 0.4 s (TN installations).
- An RCD can be used for fault protection on a TT installation. The maximum earth fault loop impedance for an RCD being calculated from the residual current rating and a touch voltage of 50 V.
I will be honest, I find the BYB difficult to use at times when trying to determine an answer for myself.
With this matter for example, I have been reading through Chapter 41 and it's sending me in circles, with one regulation referring to another and not really arriving at a clear answer.
Any input would be much appreciated.
Thanks.