Hello,

I am assisting my supervisor and getting some first hand experience of completing certification by filling in an electronic copy of an EIC, working from a handwritten circuit schedule with test results and my memories of the installation work.

I am at home so cannot ask him for advice at this moment.

This question also satisfies my broader desire to develop a thorough understanding of the correct requirements according to BS 7671.

So - I am filling in an EIC for an installation with a TT earthing system and
I am not sure what to record as the maximum permitted Zs value for each circuit.

The circuits are supplied from a consumer unit with dual 30 mA RCDs (BS EN 61008-1) and a selection of BS EN 60898 type B MCBs.

Where a TN earthing system is used, this is of course easy to do, by referring to the values in BS 7671 table 41.3.

I am struggling to understand what I should be entering as the maximum permitted values for a TT installation.
I note the following:

- The reason for calculating, measuring and checking Zs values is to ensure the correct operation of ADS.
- The maximum disconnection time for final circuits 32 A or below is 0.2 s (TT) instead of 0.4 s (TN installations).
- An RCD can be used for fault protection on a TT installation. The maximum earth fault loop impedance for an RCD being calculated from the residual current rating and a touch voltage of 50 V.


I will be honest, I find the BYB difficult to use at times when trying to determine an answer for myself.
With this matter for example, I have been reading through Chapter 41 and it's sending me in circles, with one regulation referring to another and not really arriving at a clear answer.

Any input would be much appreciated.
Thanks.
 
where an RCD is used for fault protection, due to the high value of Ze ( and hence Zs), the max. Zs value is 1667 (for a 30mA RCD). R = V/I....... R = 50V/o.03A = 1667, 50V being considered a safe touch voltage.
 
Thank you, I can see that makes sense. Re-reading regulation 411.5.3 I see it requires that the 0.2 s disconnection time (or 1 s for a distribution circuit) is met AND the resistance is low enough to achieve RCD operation at 50 V.

Although the required disconnection time for BS EN type RCDs at x1 rated tripping current is 300 milliseconds.
Of course the times achieved are often far better, in this case around 30 ms.
 
I like your thinking, you've got all the relevant points I think. :) The RCD table at the start of Appendix 3 gives maximum disconnection times at 2x I∆n of 150ms. In practice, if Zs is anywhere near 1667Ω, you've probably got other things to worry about!

Table 41.5 ultimately gives you your answer, though.
 

Reply to Maximum permitted Zs values for circuits with TT earthing system in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top