If this is an exam question then the usual supplier values quoted are:

TN-S 0.8 Ohms

TN-C-S 0.35 Ohms

TT 21 Ohms

The TT value is the sum of the resistances of the suppliers transformer winding, suppliers electrode (Rb) and the line conductor from the transformer to the consumers installation.

The recommended Ra figure varies from 100-400 Ohms depending on what publication you put your faith in!
 
And if I have a reading of 1.09 ohms on a TN-C-S system? With a fault current of 224? I'm guessing its time to tall in Western Power to get the Loop Impedance reduced?
 
If your reading is for Ze at the supply origin then yes this is high for a TN-C-S supply and this indicates a problem with either the test procedure or the supply wiring. Confirm again the result ....before calling DNO...avoids red face :)
 
And if I have a reading of 1.09 ohms on a TN-C-S system? With a fault current of 224? I'm guessing its time to tall in Western Power to get the Loop Impedance reduced?

Make sure you are taking the Ze reading with a high current, not a no-trip 2-wire test. Tested a TNC-S system today with my Megger 1730...Always do high current but thought I'd see what the no-trip gave me.. Ze=0.19 ohms 2-wire high current/1.06 ohms 2-wire no-trip.
 
Make sure you are taking the Ze reading with a high current, not a no-trip 2-wire test. Tested a TNC-S system today with my Megger 1730...Always do high current but thought I'd see what the no-trip gave me.. Ze=0.19 ohms 2-wire high current/1.06 ohms 2-wire no-trip.

Lol I did that too. DNO emergancy service operative had a 3 hour round trip and I had to call him and apologise but point out his overtime!
 

Reply to Maximum Ze Values in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

Not sure what your asking but it would require a 30 breaker
Replies
1
Views
236
I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
255

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top