Ze values on;
TNCS
TT
TNS
TNCS
TT
TNS
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Maximum Ze Values in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
The recommended Ra figure varies from 100-400 Ohms depending on what publication you put your faith in!
And if I have a reading of 1.09 ohms on a TN-C-S system? With a fault current of 224? I'm guessing its time to tall in Western Power to get the Loop Impedance reduced?
no...max Ra is 100 ohms....Tony Cable and the NIC say so.....so its got to be true...TNCS 0.35
TNS 0.8
TT = RA of 200 ohms!
Make sure you are taking the Ze reading with a high current, not a no-trip 2-wire test. Tested a TNC-S system today with my Megger 1730...Always do high current but thought I'd see what the no-trip gave me.. Ze=0.19 ohms 2-wire high current/1.06 ohms 2-wire no-trip.