Maximum zs generator and rubber box | Page 2 | on ElectriciansForums

Discuss Maximum zs generator and rubber box in the UK Electrical Forum area at ElectriciansForums.net

UPS

-
Joined
May 1, 2016
Messages
25
Reaction score
5
Location
London
Can anyone point me in the right direction.

I am working for a company who do temp power for welders etc from a generator.

We have been given a load of new boards to pre check befor they go on site. Powerlock connectors in and then D63 on a commando sockets.

I have put the maximum zs of the sockets from the table I usually use. But have just recieved an email from a member of management saying that we need to discuss the max zs values I have used (0.14).

Am I missing something?
 
View attachment 41625


This is the value I have from the generator this doesn’t seem dissimilar from what I would expect from a fixed install.
That doesn't mean that the generator can actually physically deliver that current into a fault though without the voltage collapsing and the generator stalling. Of course you will have a low impedance to the neutral/Earth link in your own generator - still doesn't mean the generator can provide that fault current.
 
View attachment 41625


This is the value I have from the generator this doesn’t seem dissimilar from what I would expect from a fixed install.

On a generator that value is not much use, that meter calculates the value it doesn’t measure it. It doesn’t take in to account any of the characteristics of the alternator or the engine.
 
I’m going to embarrass myself here and ask what a rubber box is.

?

Great posts from Davesparks btw.

Just like a waterproof box with sockets mounted on it.

[ElectriciansForums.net] Maximum zs generator and rubber box
 
I’m going to embarrass myself here and ask what a rubber box is.

?

Great posts from Davesparks btw.

Rubber box is a company who manufacture distribution units (usually referred to as distro) for temporary installations, usually made of tough rubber.
The term rubber box has come to mean any rubber distro, much the same as vacuum cleaners being referred to as hoovers.
 
You’ll need to characteristics of the generator to establish the available fault current by calculation or from the data sheet for the generator.
For all the generator setups I am involved with I use variable earth leakage relays to achieve fault protection.

Out of interest, how do you protect against Line to neutral faults?
 

Reply to Maximum zs generator and rubber box in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
223
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
683
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
625

Similar threads

  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
1K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
763

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top