Guys I have made up quick reference laminated sheets so that I do not wear out the tables on the books and as I am still learning T&I I must admit I am confused as my course at select said that I was to factor in the 80% rule of thumb from the red bok the OSG has this figure factored in but when a company came to my work to do our PIRs they paperwork referenced ZS max from the red book ?

So for clarification what figure do I use the max in the red book or the 80% figure in OSG ?

Another point also is when you meaure Ze you disconnect parallel paths so as Zs is the sum of Ze and R1+R2
then when doing this test does the parallel paths have to be disconnected to obtain a true figure ?

One last also if anybody want a copy of these tables I would be happy to pass a copy on even for some feedback
 
Hi.

The figures in BS 7671 are what is inserted on the test forms as this is what they ask for, the readings you obtain however should be no more than the 80% rule of thumb found in the OSG.

When you measure Ze obviously the whole installation is de-energised and the main earthing conductor disconnected to carry out the test.

The measured Zs is what you would find under normal serviceable conditions i.e ALL conductors connected and measured at the extremity of each circuit.
 
just wish that SOME of the expericend sparks will help with people threads and not just say u should not being doing it u r not approved there for go work in tesco for exapmle. just puts the less sparks down. every one does not know every thing about anything no matter. if u are just here to tell people how crap they are then why post??

agreed that people on here are very helpful so thank u to those
 
hi
just wanted to ask where the max zs values are for the older bs3871 mcb s are, can you use the values for bs 60898 and 61009 this is what i was told is this correct and then i x by 0.8 to get 80% values cheers
 
Last edited:
I know that 3871 3's and 60898 C's are the same characteristics, 4's and D's I've heard can be interchanged but I have never seen a Zs table for a 3871 type 4. 3871 types 1+2 are not interchangeable with any of the 60898 tables....

But I always stand to be corrected! :)
 

Reply to Maximum Zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

  • Question
Gents has anyone done an application using the UKPN smart connect portal for a split phase supply and addition of multiple single phase battery...
Replies
0
Views
398
Need to crack on to get most from this year :cool: BTW if you are thinking about adding to the strings later, i.e. add more panels to existing...
Replies
6
Views
930

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top