When completing any cert if the device was say a bs 61009 6 amp type b 30 mA would the max zs written on the cert be 7.67 ohms for a B6 or 1667 ohms thanks
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Maz zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
The maximum allowable Zs where a circuit is protected by a 30ma RCD whether the system is TT or TN is 1667 ohms. On a TN system Zs readings would normally expected to be within the range of the overcurrent device,and an excessively high zs would be unacceptable.But the fact remains that under bs 7671 the max allowable Zs is 1667 ohms for a 30ma protected circuit and so that value can be used on the cert.
agreed, but what value do you yourslf enter on the cert.? must admit, 1667 saves looking up figures in osg!
I would always insert the max permissable value fro the MCB type regardless of the RCD. Its good practice to ensure you install within the max zs values. I was called out to a boiler fault recently (ended up as an internal fault) that knocked out the RCD when it fired up. I plugged into a nearby socket to do a ramp test on the RCD, it failed to trip. I then did the full range of RCD time tests X1/2 OK, x1 OK but x5 failed to trip within time/voltage limits. Next I conducted a Zs on the socket which came back at 548M ohms!!!! Only once I had reconnected the earth supply did everything come back to realistic values.
An RCD is ADDITIONAL protection not a get out clause for either not knowing the Zs limits or not having circuits that fall within the max Zs limits.
I would always insert the max permissable value fro the MCB type regardless of the RCD. Its good practice to ensure you install within the max zs values. I was called out to a boiler fault recently (ended up as an internal fault) that knocked out the RCD when it fired up. I plugged into a nearby socket to do a ramp test on the RCD, it failed to trip. I then did the full range of RCD time tests X1/2 OK, x1 OK but x5 failed to trip within time/voltage limits. Next I conducted a Zs on the socket which came back at 548 ohms!!!! Only once I had reconnected the earth supply did everything come back to realistic values.
An RCD is ADDITIONAL protection not a get out clause for either not knowing the Zs limits or not having circuits that fall within the max Zs limits.
Even though 1667ohms is permitted I have found instances where the RCD will not trip (especially on 5X) within the prescribed time/voltage rise as per my previous post. I still put the actual max Zs as per the CB rating and if the measured Zs is higher I will investigate. If all checks out and its still high, then Ill add it as an observation on the cert.