I include a line on the Schedule of Test Results for each RCD, followed by each MCB that is fed from it.

In the Max Zs column you could put 1667 for the RCD along with other details relevant to the RCD (Operating Current and trip times), and then enter the relevant Max Zs for each MCB.

EDIT: Oops - should have read the question properly!!
 
Last edited by a moderator:
That's acceptable but the original question was referring to an RCBO device.
 
Fully agree for TT entering 1667 for max Zs, but for TN I list the MCB value and work to it as I have encountered too many sticky RCD'd as the clients NEVER do the quarterly check. By entering the MCB value, it focuses you on getting the lowest value for the MCB type.

Each to their own, its just the way I prefer to do it.
 
Fully agree for TT entering 1667 for max Zs, but for TN I list the MCB value and work to it as I have encountered too many sticky RCD'd as the clients NEVER do the quarterly check. By entering the MCB value, it focuses you on getting the lowest value for the MCB type.

Each to their own, its just the way I prefer to do it.

I think there is a mis-understanding here.....on a new circuit on a TN system I would expect the measured Zs to be well within the max value for the MCB,or other overcurrent device and would ask questions if it wasnt..(Poor design?Poor teminations?).....But on the cert I would record the 1667 ohms value as a max where an RCD protects the circuit-
A. Because technically that is the maximum allowed value...and
B. Because it saves a few seconds looking up the protective device value, and when you have a wad of certs to do anything that makes it less of a chore is to be welcomed.

I fully agree that the Zs on a TN system should be within the limits of the overcurrent device,the max value written on the cert is just academic.
That said most of the Zs values which slightly exceed the max for the protective device are on existing circuits which have been extended and altered.IMO where the excess is a fraction of an ohm over,and other tests are satisfactory,the RCD can be used to meet the required disconnection time and the slightly high Zs ignored.
 
Last edited by a moderator:

Reply to Maz zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
561
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
935

Similar threads

You would be best checking all connections as it is possible it is having a cumulative effect.
Replies
5
Views
488
For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
502

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top