Well it needs more detail like the CSA of supply cable to garage consumer? Type of cable? The route of cable? You say it’s rcd protected so do you mean it’s fed via an mcb which is in turn protected via rcd providing additional protection For multiple circuits? I would personally use an rcbo at existing consumer unit and then use double pole main switch at garage with rcbos on that consumer although nuisance tripping is a factor but Aslong as you have rcbo at house consumer it won’t interrupt the circuits at house
thanks for the reply and details. the wire to garage will be a 4mm wire in a pvc pipe (more than enough given the relatively short distance)
You say it’s rcd protected so do you mean it’s fed via an mcb which is in turn protected via rcd providing additional protection For multiple circuits?
almost like you said but theirs no mcb (by design) at that point. basically the flow is like below:
Utility Company Meter(Which some type of overcurrent protection too) ->
Main Switch A -> Surge Protector-> Over/Under Voltage Relay/Protector -> RCD (with time delay for discrimination) -> ---------Wire to Garage Panel------------>
Main Switch B -> RCD -> individual mcbs
The above is a standard setup in my country so I'm not trying to reinvent the wheel.
So as not to get out of topic, my question with reference to the above was:
"Main Switch A" and
"Main Switch B" - I have seen many(the majority) installations using a DP MCB instead of a Manual Main Switch/isolator, especially for "Main Switch B"
Also, some local shops dont even stock them in all brands and would tell you to get a DP MCB instead. And obviously I'm not very keen in opting for something just because the shop happen to have only that one...
Also
, just because many local electricians do that does not mean that its the best way.
Personally (and I stand to be corrected) I think the ideal setup would be like this:
Utility Company Meter(Which some type of overcurrent protection too) ->
Main Switch A -> Surge Protector-> Over/Under Voltage Relay/Protector -> RCD (with time delay for discrimination) -> ---------Wire to Garage Panel------------>
DP MCB -> RCD -> individual mcbs
Notes:
Main Switch A - a manual isolator is a must here because its the only sure way that the power can be switched off (a DP MCB could malfunction given that it has more components)
DP MCB - an added layer of safety for overcurrent here, because one could always used the "Main Switch A" to be 100% sure that electricity is off.
any insight would be greatly appreciated, thanks