Just looked at some Wylex and square D SP ones (all I have to hand), both only show the Icn value, Wylex 6kA on the side, and the square D on the front 6000 in the box, both 6kA types.

Other MCB's may be different.
 
Have a look at Table 7.2.7(i) on page 71 of the green On-site Guide (if you have one). All will be revealed...:shades_smile:

If you don't have the green one yet it's page 57 in the red one
 
Last edited by a moderator:
Some excellent information, Guys. Why weren't you all about when I was sitting my apprenticeship in the 70's!! And don't give me that " .... oh the internet wasn't invented then." If you have all that combined knowledge you might have invented something as simple as the internet before now!!

I was actually looking to fill in the boxes on the generic IET Schedule of Test Results. I do have the Green OSG, but I find navigating it a bit tricky yet - my synapses don't work as quickly as you young uns :)

Thanks again and ... I'll be back.
 
Not quite but almost! I remember the boss would drop everything to strip out the pipework for old gas mantles when we on rewires - it was £1 per 1LB back then and I started my time a £9.14 a week!
 
Not quite but almost! I remember the boss would drop everything to strip out the pipework for old gas mantles when we on rewires - it was £1 per 1LB back then and I started my time a £9.14 a week!




Wow, I think Noah got more than that for sailing the arc......




Just to add... The Ics is also on the Hager mcbs.

Just found one...



Jay
 
Sorry mate,

I think you will find it is the In that is marked on the device, or the nominal tripping current ie. for example Type no. B, In 6A, and as we have already said the Icn eg. 6000 or 6kA, and as Jay said, some, not all also have the Ics noted on too.

I think you are mixing up the In with Icn, we were discussing the breaking capacity, not the nominal trip rating.
 
Last edited:
No - Icn is in amperes (e.g. 6000 or 10000) and Ics in kiloamperes (e.g. 3).

I'm not referring to the rating of the circuit breaker (e.g. 32A).
 
Not quite but almost! I remember the boss would drop everything to strip out the pipework for old gas mantles when we on rewires - it was £1 per 1LB back then and I started my time a £9.14 a week!

Gents,please forgive the intrusion, can I high-jack this thread a little, just to pose a question to any "golden oldies"

What was your first wages?
I got the princely sum of 3 Pounds 1 shilling,which was handed straight over to mam,she then gave me pocket money out of it.

What was your's ?
 
you must be older than me then , des, i started on £6 odd at the start of my app.
 
Risteard,
I think we are talking at cross purposes here, the 6000 or 10000 in the little box is marked in Amps, this is the Icn value usually given as kA, eg 6 or 10 kA, the In is also marked in amps eg. 6 or 32 or whatever.

Some, but not all mcb's also have the Ics value marked on them, the Wylex and Square D single phase ones I have here do not have the Ics value marked, but some of Jay's did.
 

Reply to MCB Breaking Capacity in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

Stand to be corrected, but AFAIK you can still use rewireable 3036 fuses for a new installation, if you so desired, providing PFC and breaking...
Replies
3
Views
205
So I would say the most common example of a circuit requiring overload protection is going to be a radial or ring socket circuit. You are correct...
Replies
9
Views
823

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top