TECHNICAL BULLETIN
SAFE SELECTION OF DEVICES FOR INSTALLATION IN ASSEMBLIES
AUGUST 2011
PAGE 1 OF 1
THE ASSOCIATION FOR THE BRITISH ELECTROTECHNICAL INDUSTRY
BEAMA is warning against the practice of installing devices (e.g. RCBOs, MCBs) of one manufacturer into assemblies1
(e.g. Consumer Units, Distribution Boards) of another manufacturer.
There is evidence that some installers are mixing products, often without fully understanding the potential safety
implications.
Assemblies such as consumer units, distribution boards and panelboards are tested with specific devices installed; these
devices are more often than not from the same manufacturer as the enclosure. Testing and certification is undertaken
to BS EN 604392; formerly BS 5486. Although BS 5486 is now obsolete there are many existing installations with
assemblies complying with this standard and the issues of mixing different manufacturers devices equally apply,
particularly where older devices may be difficult to source.
In all cases installing devices other than those declared by the assembly manufacturer invalidates any
testing/certification and warranty.
BS 7671 puts specific responsibility on the installer; regulation 510.33 requires that the installer takes into account the
manufacturer's instructions.
It is, therefore, the responsibility of the installer who intends to mix different manufacturers' devices/ components in an
assembly, to undertake appropriate testing and ensure conformity with BS EN 60439. If this is not done then there is a
probability that, in the event of death, injury, fire or other damage, the installer would be accountable under Health and
Safety legislation.
Although devices may appear similar; the dimensions, technical performance and terminations are not necessarily
compatible.
Distributor and wholesaler responsibilities
A distributor or wholesaler also has a responsibility under the General Product Safety Regulations to act "with due care".
Distributors and wholesalers should be able to substantiate any advice related to interchangeability of devices in
assemblies. If the installer acts on a distributor's advice and information and in doing so produces a non-compliant
assembly then both the distributor and installer may be liable for any consequences.