hi looked at a job today 32a mcb feeding outbuiding CU. out building cu has 20a mcb for radial sockets is this ok re discrimination (mcb's in series) im sure it is but thought there was a specific ratio
 
You could always investigate a C type MCB for discrimination.
Just had this covo in a different thread no domestic mcb will give discrimination against any other under short circuit and to note the type b,c or d is inrush allowance and nothing to do with the large current that will flow in a short, i could give you the table list of partial discrimination between different size mcbs but most incoming supplies exceed this in fault current so not worth it, just have to realise its not achievable between standard mcb's.
 
If you are feeding an outbuilding with an MCB and a fault caused it to open rather than the MCB in the outbuilding, then other than the slight inconvenience of walking to the house, no other circuit would be affected. It's a different ballgame when an outbuilding fault can take out the RCD in the house and create a potentially dangerous situation.
 
Good design would put the outbuilding on its own rcbo, but if not ust make sure its not on the same circuit that has the stairs lighting on, but domestic really shouldn't fall under the concerns of a potentially dangerous situation.
 
Was a bit tongue-in-cheek darkwood. We keep being told how dangerous it is to have an RCD trip when someone is potentially walking downstairs.....
I was talking about discrimination for an outbuilding that has an RCD in its board being fed from an MCB.
 
Was a bit tongue-in-cheek darkwood. We keep being told how dangerous it is to have an RCD trip when someone is potentially walking downstairs.....
I was talking about discrimination for an outbuilding that has an RCD in its board being fed from an MCB.
Arhh! no worries but tongue in cheek is a sore point at mo! ..... i did the decent thing trying to break up a fight between 2 ppl i know last night and them been ex army it wasnt easy but i did end up with my tooth punturing through my cheek, lots of claret everywhere but feel like ive just been in the dentist chair lol
 

Reply to mcb discrimination in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

  • Article
The mcb used will be sized for the spd cable.
Replies
4
Views
405
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
327

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top