J

johndevin

Having a discussion at work ..

We are installing a 9.8 KW Shower.

If my calculations are correct this will draw just above 40A

The distribution board we are using does not fit a 45A breaker.

I think it would be safer to use a 40A than jump to a 50A.

I highly doubt the current would ever reach anywhere near 40A.

Whats your thoughts ?

P.S I know i could change the board but trying to avoid this ....
 
Last edited by a moderator:
Hi John Devin - Welcome to the Forum :)

May I ask why you think a fixed load like a shower will not pull the calculated value you arrived at?
If your load calculates above the rating of the mcb then no its not safer to create a small overload for a long duration as the reg's stipulate must be avoided. So 50amp it will be.

Are you worrying about the size of the cable here then and having to upgrade it?

PS Don't you mean 'Doesn't fit a 45amp mcb'
 
Last edited by a moderator:
i meant does not fit a 45 A breaker **

Because it will never be on maximum temp or else they might scold themselves.

I was thinking try a 40A first if it blows use an alternative method.
 
no, because it's a fixed load and yo don't need to provide overload protection, just short-circuit fault protection. 432.3 and 433.3.1 (ii). (green BS7671)
 
Last edited:
i meant does not fit a 45 A breaker **

Because it will never be on maximum temp or else they might scold themselves.

I was thinking try a 40A first if it blows use an alternative method.

You should be using and following regulations to design and wire your circuits its this that ensures the safety of the users and of the installation, I would read and listen to the advice given, TBH it's truely is disturbing reading this comment from a practising Electrician, you have to design the circuit for the manufactered stated ratings, I would also do some research on how showers actually work, most reduce flow rates to increase temperature and don't regulate the voltage to the elements so at full power it will draw the 9.8Kw and you increase the flow rate to reduce the water temp', those with 2 power setting may have 2 elements and one ised in low power.

I would also revise you time/current tripping curves and you will find that the small overload in this scenario would never trip the mcb putting you in contravention of the regulations regarding ensuring by design you do not create a small overload of the OCPD for any length of time.
 
Last edited by a moderator:
no, because it's a fixed load and yo don't need to provide overload protection, just short-circuit fault protection. 432.3 and 433.3.1 (ii). (green BS7671)

I know you are correct and wouldn't question it, I have just read those regs you have stated and can you just clarify, if its overload protection are we saying hypothetically protection of the cable / circuit from being overloaded so putting an induction hob on a 1mm light circuit for example.

And short circuit fault protection, as I read it, I may be wrong but would like you to explain, are you saying you could put a 63A or even greater so long as it falls under that reg up to PFC etc, but put an MCB on a 6mm circuit with a shower on the end that only draws 40A as its a fixed load falling with that reg as it will not exceed the specified load, so you do not need to provide protection for the cable but protection for fault only as in L-N short for example.

Is that correct?
 

Reply to MCB Selection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
401
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
989
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
789
  • Question
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...
Replies
2
Views
113

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top