J

johndevin

Having a discussion at work ..

We are installing a 9.8 KW Shower.

If my calculations are correct this will draw just above 40A

The distribution board we are using does not fit a 45A breaker.

I think it would be safer to use a 40A than jump to a 50A.

I highly doubt the current would ever reach anywhere near 40A.

Whats your thoughts ?

P.S I know i could change the board but trying to avoid this ....
 
Last edited by a moderator:
Just fit the appropriate sized MCB to protect the cable and make sure its not maxed out such as the 40A as like others say its a potential fire hazard.

No,
Select the appropriate sized MCB for the load, then select the cable size to suit.

Cable size may be based on Ib if the load is not subject to overload and fault protection is provided for the cable
 
This is my personal opinion and not to be taken as rude or bullying or as it is put, not helpful to the post etc etc

Carry out a cable calc using the regs book, if you can't do this or don't know how then there is no way you should be even contemplating carrying out the work...As you wouldn't really know what you are doing or why you are doing it and could end up with a fire on your hands....
 
No,
Select the appropriate sized MCB for the load, then select the cable size to suit.

Cable size may be based on Ib if the load is not subject to overload and fault protection is provided for the cable

Thats a swings and roundabouts way of what I said, but yes as much as I hate to say if the way you worded it was better and more accurate.
 
What make is the board? Will another brand not fit in? Often they fit ok if you get the right one.

No another brand won't be acceptable if the OP cares about doing the job properly at all. Unless the manufacturers of both the board and mcb both agree to your suggestion then the type testing etc becomes null and void.
 
I think tbh we need further input from the OP on this one or the thread is just going to go round in circles, he has had the correct advice up to press so a response from a few questions posed will be needed now.
 
@ uk sparks. ...... basically, you design the circuit to accommodate the load. so e.g. the shower is 40A fixed load. it can't draw excess current as it's fixed. so assume ref. method C, you'd select a 6mm cable (47A) so that Iz>Ib. and you'd select your MCB for fault protection, it's value according to Zs tables so as the MCB would trip within the specified time. in the OP's case a 50A type B would need a Zs value of < 0.736 ( (230/5In) x 0.8)
 
No another brand won't be acceptable if the OP cares about doing the job properly at all. Unless the manufacturers of both the board and mcb both agree to your suggestion then the type testing etc becomes null and void.

I meant more like how some brands are identical and fit exactly the same, yeah it's best to stick with the same but it would not hurt if you had one that fitted properly.
 
I meant more like how some brands are identical and fit exactly the same, yeah it's best to stick with the same but it would not hurt if you had one that fitted properly.
yup, if it's a MK board, you must fit a MK nail.
 
I meant more like how some brands are identical and fit exactly the same, yeah it's best to stick with the same but it would not hurt if you had one that fitted properly.

Some brands are just badge engineered so will be from the same manufacturer. But unless you have the paper trail to prove it you will still be up a certain creek if you mix and match
 
Some brands are just badge engineered so will be from the same manufacturer. But unless you have the paper trail to prove it you will still be up a certain creek if you mix and match

I'm not one for mixing and matching but can you explain why it's wrong to mix and match? Let's take for example a Hager MCB and a MK MCB, let's just pretend they are the same shape and fit nicely in one another's board, please explain what is so wrong about doing this other that the fact it will look different.

im bot wanting an argument just interested to hear your explanation,
 

Reply to MCB Selection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
401
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
989
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
789
  • Question
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...
Replies
2
Views
113

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top