peeko

-
Joined
Mar 14, 2014
Messages
17
Reaction score
10
Location
Derby
Hi everyone, hope you can help

Recently we've completed an EICR on a commercial property and it's thrown up some issues with the lighting. The installation method is rough as, T&E just chucked on top of the ceiling tiles as we've all seen a million times before so we'll be sorting this as part of the remedial works.

One of the issues I have is that I'm not convinced from looking at the state of it is that the cables in the walls/partitions of the office areas have the adequate 50mm protection/are inside metal conduit, therefore as per amendment 3 I've got to provide RCD protection to the circuit.

The circuits come off an old Square D 3 phase DB, and if anyone has had the misfortune to look for RCBO's that fit these, they'll tell you they're hard to get hold of and cost a small fortune. My idea is this - adequately protected cable from the current MCB to a separate enclosure of double pole RCD's, which then provide protection to each lighting circuit.

I've been told this is OK, just wondered if anybody has experience of this, pro's/con's etc? Obviously in an ideal world I'd swap the board for something more modern with RCBO's that are available/not a fortune, but for a couple of circuits I don't think they'd go with the cost of this, maybe down the line as they make alterations.

Thanks in advance
Charlie
 
Sounds like a plan to me, people often do this in domestic for new shower circuits etc.

Only thing I'd say about it is make it bloody obvious that there's a protection device after the MCB - if somebody on site needs to reset it, they may not know it's related if it's not obvious to them.

P.S. Isn't this a bit above the remit of a PAT Tester? ;)
 
:p very much above the remit of a PAT tester!

Won't be attempting myself - our sparks will be installing/testing/cert-ing, just like to make sure they're not bull****ing me at times, especially when it's a scenario I've not seen before.

Installation is about 35-40 yrs old
 
Hi Andy, they sent me 2 part codes - however every site I check says they're discontinued, not keen on putting used in off fleabay
 
"One of the issues I have is that I'm not convinced from looking at the state of it is that the cables in the walls/partitions of the office areas have the adequate 50mm protection/are inside metal conduit, therefore as per amendment 3 I've got to provide RCD protection to the circuit"


Has the client requested the code 3 work?
 
Thanks Andy, I'll have another look, might be a case of ringing round to see if anyone has any surplus stock gathering dust
 
Thanks Andy, I'll have another look, might be a case of ringing round to see if anyone has any surplus stock gathering dust

You could even ask about on here. Start a thread and see if any members have any kicking about, like you say, gathering dust. Not sure what part of the forum you would be best putting in though.

Jay
 
Schneider rcbos are readily available for Square D KQ boards. I am not so sure, if it is a QOE board that they are compatible but I could be wrong.
 
I've just recently fitted Schneider KQE RCbo Devices In a square d push fit bus bar 3 phase Board. Funny really about five years ago I sold a load of square d rcbos becaue couldn't see me using them and already go ample stock of MCB and rcbo devices. My wholesaler holds them for me. Some say ironic at what the Schneider cost in region of 50-60 quid.
 

Reply to MCB then RCD in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Adding a led strip isn't going to make much difference to the 3 phase balance. No real difference to where a 3 phase machine uses one phase to...
Replies
2
Views
365
No to all. Also would require a means of isolation for PIV - pulling a fuse wouldn't be acceptable. I don't mean to seem disrespectful, but this...
Replies
1
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top