Hi could anyone please tell me if the older push button style mcb's are noted on the test and inspection sheets as BS EN 60898 (b,c or d type) the same number as the newer style mcb's

Thanks
 
Usually the push button mcbs are BS3871 they will normally be types 1,2,3,4. The max disc times are different than bs en 60898. If they are type b,c,d then they will be 60898 and will have the same disconnection times
 
the older push button ones which sometimes replaced 3036 fuses are bs3871. the later flick switch ones are bs60898
 
Hi thanks for your quick reply, i will have to get my regs book out and look what difference the connection times are, i did look on one of the mcbs for any numbers like 60898 but they are quite old and faded, Cheers
 
The KA rated is 3 forgot to mention that. BS3871 are not listed in current regs, if you can get a yellow 16th edition they are in there but you will have to calculate them for max disc times at 230V as they are calculated at 240
 
Most probably not.
The older style MCBs were BS 3871, and were numbered Type 1, 2, 3 and 4.
The time characteristics for the old type are similar but not the same as for the new BS EN 60898 versions.
Type 1: 2.7 - 4 In, Type B: 3 - 5 In.
Type 2: 4 - 7 In, Type C: 5 - 10 In.
Type 3: 7 - 10 In, Type D: 10 - 20 In.
Type 4: 10 - 50 In.
During the change over of the standards, manufacturers were allowed to use the new BS EN 60898 designations on the old BS3871 devices, if they were within the limits specified.
For instance a Type 1 is within the specifications for Type B.
Types 2 and 3 are within the specifications for Type C.
However Type 4 is outside of the specifications for type D.
The 15th edition has time/current tables for BS3871 MCBs.
Many of the older BS3871 MCBs are only rated at a maximum of 1kA.
Most are rated at 3kA.
http://www.electriciansforums.net/a...ations-zs-values-older-protection-devices.pdf
 
Last edited by a moderator:
thanks again for your replies, i will note down the 3KA, as for the old 16th edition i think i have got one kicking around somewhere, its hard to keep up with all the regs i was told the other day i need a screwdriver with torque settings on it for doing up mcb's etc and it will also have to be calibrated every year, apparently a new reg coming out in january about it. Oh great fun more regs.
 
I think you would find the voltage relevant because the current (required to disconnect in the correct time) divided into the voltage give the max ZS values for the cpd. eg: 230/160A ( for a B32amp mcb)=1.44 ( the max ZS). When it was 240v you would get 240/160=1.5 the max ZS in the 16th. So the voltage is not irrelavent. If you get the old zs values divide them by 240 then multiply by 230 you will get the new values
 
I think you'll find that the values given in the 16th are the accurate values!! To the best of my knowledge, the UK is still being supplied with a 415/240 volt system... The new 400/230 volt band is a fictitious, paper or virtual voltage. A bloody stupid arrangement if you ask me, another example of ''Harmonisation NOT working to the UK's best interests. Or Europe come to that.... lol!!
 
I think you'll find that the values given in the 16th are the accurate values!! To the best of my knowledge, the UK is still being supplied with a 415/240 volt system... The new 400/230 volt band is a fictitious, paper or virtual voltage. A bloody stupid arrangement if you ask me, another example of ''Harmonisation NOT working to the UK's best interests. Or Europe come to that.... lol!!

nothing done by mainland europe is in the UK's best interest. now they want more billions off us to subsidise the frogs, and the krauts are insisting we scrap the ÂŁ.
 
I don't mind them Wanting, ....So long as they don't Get!!! The EU should have stopped at being a European common market. Common currency (Euro), and community laws that have nothing to do with the common market trade, as well as the European parliament is far too many steps too far, that no-one really wanted or needed!!!
 
I think you'll find that the values given in the 16th are the accurate values!! To the best of my knowledge, the UK is still being supplied with a 415/240 volt system... The new 400/230 volt band is a fictitious, paper or virtual voltage. A bloody stupid arrangement if you ask me, another example of ''Harmonisation NOT working to the UK's best interests. Or Europe come to that.... lol!!

I seem to come across 235 Volts a lot these days, maybe that's what they mean by compromise, being half way between 230 Volts and 240 Volts.

As for the European Union, a cesspit of corruption if you ask me.
 
Last edited:

Reply to mcb trip BS number help please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
919

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
  • Question
Nothing wrong with it. Which manufacturers have you got this information from? What do you mean by trip speed? Fuses and MCBs can operate in the...
Replies
11
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top