Evening,

Can someone tell me what the equation is to work out how quick a CB will trip from the Amps its getting?
I know there are tables in 7671, but I'm sure there is a formula where you can work it out from the fault current amps etc?

Thanks in advance
Craig

Are you thinking of what current will trip an mcb in 0.1 to 5s?

If so, as i=p/u said, for a B type it is 5x In, for a C type it is 10x and for a D it is 20x.
So a 6 amp C type trips in 0.1 to 5s if a 60amp fault current flows.
For a 6amp type D it would be 120 amps

edit; oops hadn't seen 2nd page where tony had also expanded on i=p/u's post .
 
Last edited by a moderator:
I don't know that i would describe logarithmic scales as easy to read - in my experience people need quite a bit of practice the first time they encounter them :)

I take it they do still teach trainee's to read time/current curves?? But yes maybe the first few times is a little daunting, but i'm sure that a qualified electrician would have no problem reading and understanding these graphs...
 
Well I'm ok with tha graph etc, I just thought there was an equation where if you had a fault current you could work out how quick it would trip?
I just want to find it for my peace of mind! been looking for hours, but if there isnt one then my mistake!

If all your trying too find is disconnection times you been given the Method.

example

6 amp type B, so 5 x 6 = 30 amps, so as long as you have more than 30 amps you know it will disconnect at least with .4 of a second.
 
eg voltage divided by say if 60898 type B (5 times rating of braker eg 32A)
so 230/(5*32)= 1.44 ohms
so 230/(5*1.44)= 32A
Type B 5x, C 10x, D 20x.

Also as Chr!s says.

any good for you
 
Last edited by a moderator:
Isn't this information also given in the time/current curves of each type of protective device in an adjacent block, showing MCB/fuse ratings and the required current to achieve disconnection times?? I'm sure it was in the 16th edition...
 
Thanks for the replies.
I'm ok with B,C type and their tripping times/currents etc, I just thought there was a formula where by you had a fault current and a CB rating, and you could calculate the CB's tripping time.
Not to worry
 

Reply to MCB tripping time equation? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
812
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
986

Similar threads

So I would say the most common example of a circuit requiring overload protection is going to be a radial or ring socket circuit. You are correct...
Replies
9
Views
826
Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
964

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top