wallyanker

Hello Guys/Gals

I was called out to a shop yesterday to look at a faulty heater. Whilst I was there, I noticed that to turn the 3 rows of 8 foot fluorescent lights off, the shop staff use the 16a mcb's in the fuse box, 1 mcb per row. My understanding from the regs book is that a mcb should not be used for functional switching. Can someone confirm I have read this correct?

Thanks
Pete
 
Thanks mogga, I'm gonna go back and fit light switches for each row. Think there is 4 double 8 footers per row so was thinking of fitting a 3 gang light switch.

Thanks again
 
Thanks mogga, I'm gonna go back and fit light switches for each row. Think there is 4 double 8 footers per row so was thinking of fitting a 3 gang light switch.

Thanks again

You might suggest replacing the fittings as well as it is going to be hard getting 8' lamps in the future.
 
Where in the regs does it state mcb's cant be used for functional switching?, most modern mcb's have a switching capability (mechanical life) in the hundreds of thousands, also i would check the wiring complies as 16amp would be pushing the bounderies for even a 1.5m^2, so check if its cable calcs comply or is it wired in 2.5mm^2.
 
Last edited by a moderator:
Just confirm SirKit Breaker there, Table 53.2 states a circuit breaker (be it BS EN 60898, BE EN 60947-2 or BS EN 61009-1) are all acceptable to be used as functional switching.
 
Thank you to all for the information. It just doesnt seem right that opening a cupboard, flipping down the front of the consumer unit and flicking the 16a mcb off is an acceptable way of turning the lights on and off.
I'm going to fit normal light switches anyway for convienence and because I think it is the proper way to do it, I don't think the shop assistant girls should be turning mcb's on and off every day.
 
Thank you to all for the information. It just doesnt seem right that opening a cupboard, flipping down the front of the consumer unit and flicking the 16a mcb off is an acceptable way of turning the lights on and off.
I'm going to fit normal light switches anyway for convienence and because I think it is the proper way to do it, I don't think the shop assistant girls should be turning mcb's on and off every day.
Well its your call but i think its just the way you are thinking that deters you from using mcb's to switch, if you actually think about it the mcb (60898 i suspect) is more robust and durable than the light switch you intend to put in, and a light switch would only be required if their is a health and safety risk of trying to get to the mcb in the dark to turn the lights on and in this case putting remote switching in is justifiable.
 
In some ways its not acceptable. You just have to trim the fat to find the right reason. Stating that you simply cant use the MCB is incorrect as the regs can prove. However you could maybe consider the use of the installation with regards to the competency of the user. You could find reason, depending on the layout to suggest that only skilled persons should be able to 'avoid dangers that electricity may create', which regular access to the CU may introduce.
There could be other things to consider like access etc also....
 
There is also a risk to the business if there are other circuits in the fuse box, e.g. what if someone's hand slips and they accidentally switch off a circuit, possibly not even realising they have done this. Or accidentally turn on a circuit they didn't intend to.
 
I remember years ago, not sure if it's the same these days, but we installed "Police lighting" direct from the MCB. These light's were designed not to be switched off at night, but perminently left on. From memory, the design showed one row in four would not be switched off. Could this be the same sort of thing??
 
Had a recent em light test where every fitting failed after 10-15mins then lassie told me she was told to turn off mcb to put all lights out as switches only turned out some the ones left on were the Police lights which had a key switch but them being bean stackers just thought leaving lights on all night was burning money
 

Reply to MCB used as light switch in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
54
  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
384
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
346

Similar threads

I fitted a Mem MR30 Pod and MCB, about £75 for both.
Replies
8
Views
2K
Yes I understand the setup now. Sorry about my confusing first post 🫢 It might be worth buying the Livolo switches you identified and lash at...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top