MCBs on.. But still power? | on ElectriciansForums

Discuss MCBs on.. But still power? in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jul 15, 2018
Messages
12
Reaction score
6
Location
London
[ElectriciansForums.net] MCBs on.. But still power?


Hello all,

I've searched the forum before asking but coming up empty handed??

I have a power cut from earlier. Live in a flat with a joined kitchen / living room and heard a bang from around the boiler area, then darkness.

Checked the CB's and had 2 tripped which were "B circuits" and lighting. The main 100A MCB was still in, but no power anywhere in the flat.

I've put both CB's back in and still nothing. I have no CB's off now but still the flat is dead. Checked with neighbours as I thought maybe it was the supply and we were all down but they're good. So MCB in and subsequent CB's in but still nothing... Can anyone please advise?
 
Your board looks like it’s fed by an armored cable (black one entering the board at bottom) this means the meter is probably external to your flat? If so go to your meter cupboard which is probably in the communal area and there will probably be a switch fuse or circuit breaker supplying your flat. My bets would be it being a circuit breaker that’s tripped by your meter because if it was a fuse I doubt it would of blown.
 
Just for future reference, the red 100a main switch is only a switch, it will never trip on overload or a short circuit fault.
As Westward10 has asked a good question, if the yellow buttons cause the RCDs to trip....then there is power present at the DB, if they don’t, then you have no power.
 
Cheers. Tried to find it but think it's downstairs in a locked cupboard which I can't get access to (no access to meter as is inclusive with tenancy.)

Waiting on someone coming out to it, but that's been since around half 5, so guessing won't see him or her tonight.

Yeah, cheers snowhead, I would've switched them all off before I did but since can't get access I'll need to wait it out.

Westward 10; I did try resetting them but nothing.
 
Hi @enpassant just to while a few minutes away while you are there candle in hand awaiting succour, En Passant, I am teaching my grandsons chess and was trying to remember exactly how the En Passant rule worked, do you know?
My chess skills are so basic I had to ooogle that up. But if anyone tried that stuff on me I'd definitely have to resort to harsh language...
 

Reply to MCBs on.. But still power? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
877
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top