Can you adjust the time lag coefficient on the MCCB? A small mains blip shouldn’t cause nuisance tripping.
What’s it going out on over current or under voltage? I had a problem with U/V on an ACB a few years ago, 2ms delay solved the problem.

Many thanks Tony,

I will have a look at the calibration settings when on site and take it from there.
Some units have 2 dials covering trip threshold marked In and Io, others are even more flexible with 3 dials, the third covering Isd which I believe is the prospective fault current.
i usually multiply the nominal rating set on dial 1 Ir by the Io and Ir calibrations.
Any other info would be much appreciated, but my guess is they have been gradually increasing loadings, and as a result a loss of power, even though momentary would mean a sudden surge through the device which would re instate under full load is causing the tripping. So hopefully re calibration could well be the answer. They also need regular checks on the system to ensure max demand criteria remains within the design parameters of the install, but you would think that would be common sense.
 
That old chestnut again, has anything changed? No! Well, we added this and that and oh, that other bit, but nothings changed! (Well it’s only bits of stuff).

A different scenario but I had to up rate an ACB from 800A to 1200A and add a 3rd feeder cable etc. But nothing had changed! Someone sneaked the 300HP compressor in under the cover of darkness!
 
Aint that the truth Tony, Often with the bigger companies, they have various contractors adding here and adding there with no one keeping check on who's doing what, where and why. I remember on one site Red phase had 80 amps Yellow 260 and Blue 140. But it happens all the time, at least on this one the phases are pretty well balanced so no issues there. Thanks for the responses to all.
 
Is it possible to add an alarm
To call maintenance if the mccb tripped

It’s a bit late by then, the problem has to be stopped before it starts.

Quote the plant manager “did you know the main breaker’s tripped again?” Me “yes the fu**ing kettles stopped boiling and it’s bl**dy dark in here!”

Discrimination and trip settings are a nightmare when you get to 400A+ breakers, as Baldsparkies obviously knows. Both time and current are adjustable so it’s easy to alter one setting on the local breaker and move the problem one step up the ladder.
 
Last edited by a moderator:
Aint that the truth Tony, Often with the bigger companies, they have various contractors adding here and adding there with no one keeping check on who's doing what, where and why. I remember on one site Red phase had 80 amps Yellow 260 and Blue 140. But it happens all the time, at least on this one the phases are pretty well balanced so no issues there. Thanks for the responses to all.

Very true mate. the sites im working on, nobody has a clue whats in them and what isnt. half of them are not even fully functional, and trying to find out anything ie teste results ect, is a nightmare.

at the moment, they have employed another frim to carry out PIR's, but they are also testing our firms half finished installs, failing them, as they are not complete, and ive still got to test them when they are fininshed. i reckon that the firm will bill for remedials, and when thhey turn up to carry out the work, wuill find it all kosher, cos we would of finished, and earn for nout.

its a shame that electrical safety isnt a priority.
 
ill try and get some photos of some of the gear i see. its ancient, but sill works. in one place there are 2 massive generators, one english electric, and one blackstone. they have DC generators at the end, on the same shaft, which i guess are being used as exciters. a small petrol engine acts as the starter. its a shame, but both of these beasts are no longer operational. the panel for the blackstone genny must be 50's, and still in good nick. ive opened some of the cubicles, just tp noes at the wiring, and its the neatest ive ever seen.
 
Would be interesting to see Johnboy. The fact there still operational is testament to the quality of build with the old stuff,
I mean look at me. Born in 1953 and still going strong, keep tripping over the zimmer frame though.:D:eek:
 
I was heart broken to take this out and replace it with modern crap. Just a pitty I didn’t get a picture of the front, polished black slate

View attachment 5718

We even had a mercury arc rectifier.

Meet Rodney

View attachment 5719

Used to scare the living daylights out of me at first, but then I got quite fond of it. To watch it working was like watching a living thing.
 
Last edited by a moderator:

Reply to MCCB vs HRC overcurrent protection in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
403
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
991
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top