Got a Ze of 0.6 ohm on a TN-S.
Circuit protected by a 250 amp mccb with an operating Zs of 0.073 ohms. Any ideas what I can do? Any advise much appreciated.
 
Got a Ze of 0.6 ohm on a TN-S.
Circuit protected by a 250 amp mccb with an operating Zs of 0.073 ohms. Any ideas what I can do? Any advise much appreciated.
How would we normally go about improving Zs? We can't improve Ze so we're either going to be upgrading cable size, upgrading breaker size or smaller circuits/runs; any of these a possibility?
 
Last edited:
Investigate why the Ze is that high, assuming it is a supply > 250A then the PSCC ought to be 5kA or more so it must be related to the earth arrangement.

If there is no reasonably way to fix that, look at the RCD add-on for the MCCB, set to 1-5A or whatever supported trip current with delay 0.5s or so and you meet earth fault disconnection as well as selectivity with any down-stream boards using 300mA S-type RCDs..
 
Investigate why the Ze is that high, assuming it is a supply > 250A then the PSCC ought to be 5kA or more so it must be related to the earth arrangement.

If there is no reasonably way to fix that, look at the RCD add-on for the MCCB, set to 1-5A or whatever supported trip current with delay 0.5s or so and you meet earth fault disconnection as well as selectivity with any down-stream boards using 300mA S-type RCDs..
Think the rcd add on is the only option, DNO said Ze is what it is, helpful as usual
 

Reply to MCCB Zs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
260
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
701

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top