As an example - on a data sheet I have in front of me. Sharp NU-180

Graph is a bit coarse, but @ 1000W/m2 Voc = 30.2V
@400W/m2 Voc is in the region of 28V - thats a 7% difference - which adds up to what you're getting.

Difficult to guess what irradiance you got, would depend on time of day and even where you are!
 
sorry but i have a slight memory issue, if there are 2 strings one with 9 panels and one wit 7 on, will the Isc that you measure/calculate be the same on both? or one slightly higher?

 
Hi YellowVanMan

I would appreciate help with f43 form for MCS if you would? My number is 07745 304179 or [email protected]. I'll phone you back. It's just a couple of the boxes I don't quite understand.

Cheers Phil
 
Hi Dan, I have my MCS assessment booked on Tuesday and I'm just in the same position reaching total confusion. I'm seeking help for a 3.8Kw, 190w 20 panel, 2 string system going into a Fronius IG plus 35 inverter, which can only be described as a beast of a unit.
I have gone down the easy MCS route, but unsure what is required and which forms to fill in for the assessment.
many thanks
Paul
 

Reply to the thread, titled "MCS Array test help" which is posted in Solar PV Forum | Solar Panels Forum on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top