Evening chaps, thought I'd post this here to help potentially successful trainees in the future as I'm 99% sure this isn't covered in the courses (certainly not in mine anyway).
Measuring Ze and Zs is straight forward, and we all have in our heads Zs = Ze + (R1+R2) BUT what about measuring these at sub mains? I've heard of taking the usual Ze and adding this to the R1+R2 supply to give you the "Zdb" for that particular DB then using that Zdb as the Ze for the next DB and adding its circuits R1+R2 giving you the Zs. However how can you take a direct reading of Zs from a sub main circuit? I gave it a whirl on site today and ended up with ~180Ω from a socket outlet which clearly isn't right, it's TN-C-S btw.
Setup goes: DB1 > RCBO > DB2 (which has it's own RCD covered circuits).
As far as I'm aware we're shown measuring Zs and Ze and their relevance to R1+R2 but only at a single DB.
Cheers in advance!
Measuring Ze and Zs is straight forward, and we all have in our heads Zs = Ze + (R1+R2) BUT what about measuring these at sub mains? I've heard of taking the usual Ze and adding this to the R1+R2 supply to give you the "Zdb" for that particular DB then using that Zdb as the Ze for the next DB and adding its circuits R1+R2 giving you the Zs. However how can you take a direct reading of Zs from a sub main circuit? I gave it a whirl on site today and ended up with ~180Ω from a socket outlet which clearly isn't right, it's TN-C-S btw.
Setup goes: DB1 > RCBO > DB2 (which has it's own RCD covered circuits).
As far as I'm aware we're shown measuring Zs and Ze and their relevance to R1+R2 but only at a single DB.