Spearmint your just a little muddle up thats all, you are almost there, just need to clear a few thing up with in the morning. too late now I'm off to bed but if you are loosing sleep over this, dont! It will all be clear this time tomorrow (having a day out with family, back on in the evening).
 
Yeah no worries, certainly not loosing any sleep over it. Maybe I'm going around in circles with this but to measure the Zs of this particular RFC it has to be energised, and for that to happen DB1 must also be energised. Both DBs are covered by RCDs so using the plug top adapter and setting the meter to the relevant no trip current (30mA in this case) is the only way I can think of doing it. Obviously you can use probes into the back of the socket but this would yield the same results surely?

How else can it be measured under live conditions?

Sigh, I'll forget about it for a bit lol. Have a good day all!!
 
When taking a Zs you need a complete circuit (Loop) down the CPC, back down the main earth, back to the transformer and then back through the phase conductor to the point of the fault. Have you tried any other sockets? Their might just be a high impedance on the circuit mate which the tester is picking up. When you do a loop test you can either do high loop which sends 25Amps around the circuit, or a no trip which will send 15milli amps down the circuit. A 30ma RCD can trip anywhere between 16ma and 30ma and comply I believe. I would try taking a test from other sockets on that circuit and also at the DB.:)


These loop test currents may vary with different testers. The values i have used are for a Megger 1552/3.
 
Last edited:
When taking a Zs you need a complete circuit (Loop) down the CPC, back down the main earth, back to the transformer and then back through the phase conductor to the point of the fault. Have you tried any other sockets? Their might just be a high impedance on the circuit mate which the tester is picking up. When you do a loop test you can either do high loop which sends 25Amps around the circuit, or a no trip which will send 15milli amps down the circuit. A 30ma RCD can trip anywhere between 16ma and 30ma and comply I believe. I would try taking a test from other sockets on that circuit and also at the DB.:)


These loop test currents may vary with different testers. The values i have used are for a Megger 1552/3.
Tried it on all twelve socket outlets, all give the same reading within 0.2ish of each other. It's a really bad first example in a way because I've yet to carry these out on the course but on site ended up with silly readings. I'll be taking a Ze next time I'm there but that isn't going to change the measured Zs from the sockets which are high. It isn't even exclusive to the one circuit either, there's two separate RFC from the new board and they also have the same high readings.
 
Like you said, do a Ze when you go back and establish that it is within 0.35 ohms(TN-c-s) if you have a good Ze the you know the problem is within the installation, just a process of breaking it down until you find the cause of the high reading.

Its all good practice and experience :)
 
Like you said, do a Ze when you go back and establish that it is within 0.35 ohms(TN-c-s) if you have a good Ze the you know the problem is within the installation, just a process of breaking it down until you find the cause of the high reading.

Its all good practice and experience :)
Will do. I fear this could open a can of worms though... main board has been in for years, if the issue turns out to be from the main board then... ah fun times lie ahead! :)
 

Reply to Measuring Zdb in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
260

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top