When taking a Zs you need a complete circuit (Loop) down the CPC, back down the main earth, back to the transformer and then back through the phase conductor to the point of the fault. Have you tried any other sockets? Their might just be a high impedance on the circuit mate which the tester is picking up. When you do a loop test you can either do high loop which sends 25Amps around the circuit, or a no trip which will send 15milli amps down the circuit. A 30ma RCD can trip anywhere between 16ma and 30ma and comply I believe. I would try taking a test from other sockets on that circuit and also at the DB.
These loop test currents may vary with different testers. The values i have used are for a Megger 1552/3.