Hello there,
I have a megger MFT 1552 tester and have an enquiry to the non-trip Zs test.
I understand that a higher result on the non-trip test, when compared to the standard LOOP test can be obtained.
What I would like to know is:
a) Why this is (I'm thinking something to do with applied test currents)?
b) What level of inaccuracy is deemed acceptable by yourselves? This is so that I can monitor the inaccuracy when self checking and understand when to get them checked out if necessary.
Many thanks
Hi David,
The MFT uses a 15mA test current live to earth on the no-trip range with an accuracy of +/- 5% +/- 0.03ohms. It also has +/- noise margin due to the low current. The hi current range has the accuracy +/-5% +/-0.03ohm. So it is the noise margin that causes the difference in reading. I would suggest appliances are disconnected from the circuit under test and any heavy loads on the circuit or nearby circuits are switched off to keep the noise down.
Check boxes are a good way of checking the calibration of your testers. I have attached a data sheet for our MTB7671 which you can use to check calibration as it stabilises the loop reading of where the check box is plugged in.
Regards,
Kerry Burdett
Dover Technical Support
Megger Limited Archcliffe Road Dover
Kent CT17 9EN England
Hi Wilder
i am totaly buggered, my initial question to meggar was, why my new tester is giving a higher reading than the ze + R1 +R2 an non trip test of zs.
they suggest it is due to the rcd.
further to this i then ask, is it a case that zs does not allways equal ze +R1 +R2 within reason.
but also the result i put on the cert for zs is not the one i get from the tester but rather the calculation of R1 + R2 + my ze reading.
god help me
Just to Add, I have a 1552 and testing a circuit prior to a new board change had a loop on a ring circuit of 0.53.
After swapping the board and carrying out my test, I tested the same socket and got a reading of 1.03ohms. I called megger and after reporting the issue a very knowledgeable gent got back to me and said this seemed to occure when certain Manufacturers RCD's were installed (something to do with the coil size and greater resistance). I swapped the board out again from the Hager board to an MK board just to see if this was correct and sure enough I got a reading on that socket of 0.58 which was near enough for me! Anyone else had this issue ?
Yes.
Different devices can create different levels of impedance. This is one of the arguments against the NICEIC's new strategy saying would should only calculate Zs values for circuits where working live would be required in order to take a measurement.