In training at the moment just brought a Megger 1553 can anyone tell me how to connect to establish the PSCC at origin - I have done
the earth using 2 leads red - line \ green - earth and reading was 4.7Ka

When I then move the green to the neutral reading shows <1 A - what setting should the meter be on and how are the leads
connected - the detail with the meter states that 2 leads can be used

Thanks Trev
 
it's a 2 lead test. have you got the leads correctly connected in the 1553? if the earething is TNC-S, the pssc and pefc should be the same.. readings taken with all earths and bonding connected, unlike Ze wher the main earth is dissed.
 
PFC – Prospective Fault Current


Made up of PSCC and PEFC


PSCC – prospective short circuit current
PEFC – prospective earth fault current (230v/Zs = PEFC)





  • Change meter to PFC ( Hi ) ( LAST GREEN SETTING )
  • Connect one probe to earth bar and one to line PEFC
  • note reading
  • Connect one probe to tail of Neutral & one to line (in) PSCC
  • note reading
  • Put Consumer Unit Cover Back On


The highest value should be of these 2 should be lower than mcb rating ie. 6000 or 10000 ;
 
I may have this a bit wrong, and just flogged my 1553 to get the 1730.....

but IIRC early 1501s had 3 settings and the later 1501s and 1553s had 4 settings...

Ze and PFC low, which is a 3 lead test for RCD protected ccts
Ze and PFC high, which is a 2 lead, red and green test at 25A (?)

the test basically is live-earth then, live-neutral and record the highest value... should be the same for tnc-s

it sounds like your lead isn't connecting very well, I have found that megger leads sometimes don't work great when probing onto the screws on the main switch or breakers
 
Hi

In training at the moment just brought a Megger 1553 can anyone tell me how to connect to establish the PSCC at origin - I have done
the earth using 2 leads red - line \ green - earth and reading was 4.7Ka

When I then move the green to the neutral reading shows <1 A - what setting should the meter be on and how are the leads
connected - the detail with the meter states that 2 leads can be used

Thanks Trev

You are measuring on the incoming side of the main switch when testing for PFC L-N. Done it myself in the past and had the same reading.
 

Reply to Megger 1553 & PFC in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
Complete guess, but it's probably cheaper to let a separate meter read a CT clamp and send the data to the charger's microcontroller using rs485...
    • Like
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top