Hi, I have a megger 1741+ that won't perform the 1kv IR test.
Everything else on the tester is good but when I press test with 1kv IR settings it triple beeps, that's with the leads not connected to anything (or connected to a circuit).
Is there an easy fix for this or does it need sending back to megger?

Thanks
 
Can I check something - on Megger's IR testing is press and hold the test button, and for 1kv there is a delayed start for safety.
Are you pressing and letting go or pressing and holding?
 
Ahhhh, thank you! Just have to hold test through the warning beeps and it carries out the test... 🤦👍
Good stuff. That's a decent tester you have there.
When doing routine IR tests at 500v and 250v, still press and hold. My boss used to say 'don't be afraid to warm things up!'
Seeing how the IR changes with time can be informative, e.g. if the results improves the longer you hold it can suggest the test is drying out moist or damp cables.
 

Reply to Megger 1kv IR faulty? in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

No. Chauvin Arnoux wouldnt play ball. I thought I had sussed with the capacitors but no. We've too busy with work since to really look into it.
Replies
2
Views
799
Well done. Leads sound a bit high btw mine are 0.07 when warmed up. Rcd uplift - I either calculate Zs, or use the kitcher trick. See
Replies
13
Views
3K
  • Question
I've discussed this with the OP directly as we are friends, but for anyone searching in the future, the service manual suggests that this...
Replies
2
Views
747
That is very cool. It would be the end user software that would make that the absolute king.
    • Winner
    • Like
    • Informative
Replies
1
Views
376
  • Question
Mice are one option, as in they might have nibbles both L and N over a segment, but most circuits seemed OK so far and no other evidence of an...
Replies
13
Views
1K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Trending Electricians Tools

New job, new tester; Megger 1741+, those that have one; anything good/bad to report? Work also trusting me with a Flir E5 magical heat-reading...
Replies
210
Views
95K
Absolutely correct they hold water, shrouds are totally unnecessary. 20s is 24mm spanner, 20 large is 30mm spanner.
2
Replies
41
Views
45K
If that little thing, plugs your butt, you better eat slowly. 🤣
    • Like
2 3 4 5 6 7 8 9 10 11 12 13 14
Replies
336
Views
41K
B
I'd say everyone has knowledge gaps in their area of electrical work I know i have quite a few i work on to fill them in
2 3 4
Replies
75
Views
29K
I too have been tempted.. I’m buying for my son. He’s in his2nd year at collage and looking for apprentiship. Sadly it’s almost impossible in my...
Replies
11
Views
25K
Of course. “Ye canna change the laws of physics” EDIT. oh blimey, I just spotted the date of the OP. ? Thank you very much @Lord lee jan You...
Replies
40
Views
23K
Only way to do it in a tight space
2
Replies
33
Views
21K
The display on the Mft pro is not very durable mine is broken already 😡
2
Replies
29
Views
21K
Only lawyers , solicitors and dodgy chat up lines charge for picking up the telephone 🙃
2 3 4
Replies
97
Views
20K
J
I'm not entirely certain as it's very tough, but brittle when cold.
2 3
Replies
65
Views
19K
nicebutdim
N

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks