hello guys
My megger kept tripping out a Wylex 10a RCBO today, the circuit i just installed and polarity had been checked at evey point i don't understand what the problem could be? I obviously set the meter to no trip
i assume you were diong loop tests. did you connect all 3 leads in the right order.?
I'm playing all the right notes, but not necessarily in the right order. Eric Morecambe
if doing the test with loads connected, could be that there is some leakage on the circuit and the 15mA that the megger puts into the test takes it over the RCBO's threshold.
Please see photo, FYI
[ElectriciansForums.net] Megger kept tripping RCBO
I've had bother with wylex rcbos tripping on loop tests before, I remember now the only way it stayed on for the test to work was to remove all load from the circuit. I've carried out loop tests before on other makes of rcbos with load on and they don't trip.
Reply to Megger kept tripping RCBO in the UK Electrical Forum area at ElectriciansForums.net
Yes that was me. If you change your mind give me a shout and I’ll sort something out for you 👍
I've discussed this with the OP directly as we are friends, but for anyone searching in the future, the service manual suggests that this...