bororich

hi guys...
i have been testing lately and have found my megger 1553 has been giving me higher r1+r2 results than the Zs results... i use the same leads, always use good batteries and have it calibrated? is the machine at fault? has anyone ever had similar experiances? im aware that there maybe parralell earths aswell but it is happening too often to be that...

please help!
 
Check you not getting confused by parallel earth path like metal conduit, armour, trunking or metal building structure if linked to the back of a metal box?
 
yeah i have checked this there is no parallel earth path on this circuit i did today.... twin and earth cable into a plasterboard box.. it has really confused me? mates at work are stumped too!!
 
Its probably just a poor connection only showing up when you do the ohms test off the battery in your meter, as the mains voltage 200 plus volts more than the battery test and is not showing this problem.
The cables are all probably in and screwed bit one probably needs tweaking tighter.
 
i will replace the leads and get back to you.. they seem fine visually but i will swap them for another set. thank you for the advice
 
Hi

You have stated you have changed the batteries, so after checking the test leads it is possible the unit may have a fault.
Have you noticed any difference in readings between the mains test lead and the 3 individual leads?

Regards

Megger TSG
 
mine does the same on no trip but ok on high i think it uses the neutral on no trip as the other day i had a skt with no earth on high it came up 55v well no response when i put it on no trip it took a reading
 

Reply to megger strange test readings... help!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
344

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top