Customer has this 110KW (converted to 55KW) motor powered via a generator.
They had a problem with the generator cutting out on startup showing overload fault.
Having investigated this issue, along with the motor overload having been bypassed!! (will be rectifying this!)
when I took the cover off the motor I noticed the nylock nut had melted its plastic with signs of overheating.
whilst removing the link bar to test the coils, I found the whole terminal post had melted out of the insulating section. and pretty corroded terminals.
My assessment is a poor connection on the terminal posts .
The coils seem ok.
Im trying to get a motor expert to come out and give his opinion and repair option. however having trouble getting someone out quickly, and customer needs this running ASAP.
Can anyone think of a temporary or permanent, safe fix?
I guess it really needs new terminal block and posts?
What do you guys think?
They had a problem with the generator cutting out on startup showing overload fault.
Having investigated this issue, along with the motor overload having been bypassed!! (will be rectifying this!)
when I took the cover off the motor I noticed the nylock nut had melted its plastic with signs of overheating.
whilst removing the link bar to test the coils, I found the whole terminal post had melted out of the insulating section. and pretty corroded terminals.
My assessment is a poor connection on the terminal posts .
The coils seem ok.
Im trying to get a motor expert to come out and give his opinion and repair option. however having trouble getting someone out quickly, and customer needs this running ASAP.
Can anyone think of a temporary or permanent, safe fix?
I guess it really needs new terminal block and posts?
What do you guys think?